AMT messages stop after re-installing I/NET
  • AMT messages stop after re-installing I/NET
‎2018-09-07 03:40 AM
Last Updated: Crewman ContentModerator ‎2025-09-25 02:32 AM
AMT message stop coming through after re-installation of I/NET
TAC INET
I/NET Seven all revisions.
If you re-install I/NET from a clean install.  That is you have uninstalled I/NET initially, AMT masking is cleared from the Host PC.
  1. Go to AMT Configuration (Edit > Configuration)
  2. Select the correct distribution group and mask settings for the site
  3. They must match the source points so that you receive the correct alarms and messages for that Host PC. For further information refer to TCON 299 - Chapter 6 "Message / Alarm and Printer Masks"
If this still does not resolve your issue then refer to article AMT not receiving Data for additional items to check.
  • TAC INET
  • 4271