Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Smart-UPS & 1-Phase Symmetra

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • Network Management Cards
  • Network Management Card 3
  • Smart-UPS & 1-Phase Symmetra
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • EcoStruxure IT Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

NMC Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support

Smart-UPS & 1-Phase Symmetra

Sort by:
Views
  • Date
  • Views
  • Likes
Options
  • Subscribe
  • Bookmark
  • Invite a Friend

Release Notes for Smart-UPS & 1-Phase Symmetra Firmware v2.5

Affected Revision Levels   Component  File Details Smart-UPS Application apc_hw21_su_2-5-0-6.nmc3 UPS Application for Smart-UPS, Smart-UPS RT, Smart-UPS VT, MGE Galaxy 3500. Symmetra Application apc_hw21_sy_2-5-0-3.nmc3 UPS Application for 1-Phase Symmetra, Symmetra LX.   For details on upgrading the UPS Network Management Card 3 (NMC 3) firmware, see the NMC3 User Guide. NOTE: If you upgrade to firmware version 2.0 or later, you cannot downgrade to a firmware version lower than 2.0.   New Features   New Feature UPS Family Smart-UPS 1-Phase Symmetra SNMPv1 port number is now configurable. ♦  ♦ Support added for Dell VxRail for PowerChute Network Shutdown 4.5 or higher.   ♦ Security Updates The default value for Bad Login Attempts is now 5. In previous firmware versions, it was 0 (unlimited). If the number of Bad Login Attempts is exceeded, the user account will be locked out for 1 hour, or until the Super User or other admin-level account unlocks the account. The Web UI now reports "Invalid username or password" instead of "Account locked out" if the number of Bad Login Attempts is exceeded. These security updates affect all user accounts, including the Super User. ♦ ♦   Fixed Issues   Fixed Issue UPS Family SRTL Devices 1-Phase Symmetra The Network Interface on the NMC3 is communicating as expected. ♦ ♦     Hash Signatures   Signatures apc_hw21_sy_2-5-0-3.exe CRC32 FD350429 CRC64 2D3E12837A5AFB34 SHA-256 DA456C31CBA96971F5DC12D3B5B6B7A8F0332A5A9012DA513667BAAB120AD25B SHA-1 244DA6048A587BA78CB991F3AA97BBFE84205089 BLAKE2sp D478080AD2A59FBBAAA9F0E95F404BA752B8E57E841F149654E16802F636EB58     Signatures apc_hw21_su_2-5-0-6.exe CRC32 F8E22A16 CRC64 9EE5E803F84A30D0 SHA-256 9534F80631CF760F7C725446A8EEAECCA7DCF59302103E46C1E6DB9BD7B487E3 SHA-1 1A8A2F7E0942D4500CDE375D4E7C5CAEFA5E7120 BLAKE2sp 7BE54C58D5C4B84ACADEE7A2A5EBB0986EFB19A958CCC0A7A4584E5E9EAF478B
View full article
Lt. Commander SwathiNaidu Lt. Commander
‎2024-06-18 03:54 AM

5521 Views

Release Notes for Smart-UPS & 1-Phase Symmetra Firmware v3.2

Affected Revision Levels   Component  File Details Smart-UPS Application snst_nmc3_su_3-2-0-8.exe UPS Application for Smart-UPS, Smart-UPS RT, Smart-UPS VT, MGE Galaxy 3500. Symmetra Application snst_nmc3_sy_3-2-0-7.exe UPS Application for 1-Phase Symmetra, Symmetra LX.   To upgrade to firmware version 3.0 or later, the only supported method is the Secure NMC System (SNS) Tool, which can be downloaded from www.apc.com/secure-nmc or by searching for SFNMC3FMTSU. To access the firmware in the software, a valid Secure NMC subscription is required. For more information, see the SNS Tool User Guide.   NOTE: If you upgrade to firmware version 2.0 or later, you cannot downgrade to a firmware version lower than 2.0. If you downgrade from firmware version 2.4+ to a firmware version lower than 2.4, this will cause the card to be formatted, erasing all security certificates, encryption keys, configuration settings, and the event and data logs.   New Features   New Feature UPS Family Smart-UPS 1-Phase Symmetra The NMC3 platform and Smart-UPS and 1-Phase Symmetra applications are now IEC 62443-4-2 SL2 certified; a higher level of certification than SL1 announced in October 2023. ♦ ♦ Support added for optional Spot Fluid Sensor (NBES0301).   ♦ Support added for configuring Universal I/O sensors via the cfguio command on the Command Line Interface (CLI).   ♦ Support added for audit logging to ensure that control actions and configuration changes are recorded in the Event Log.   ♦ Security Update Support added for integrity checking of the configuration file. ♦ ♦   Fixed Issues   Fixed Issue UPS Family Smart-UPS 1-Phase Symmetra SSH and Telnet sessions now terminate as expected. ♦ ♦ The Web UI now supports the Primary and Secondary DNS fields with a maximum of 40 characters. ♦  ♦ An error no longer appears when trying to access certain Web UI pages as a Network-Only user. ♦  ♦ NMC no longer reboots when configuring 'Controlled Early Shutdown' parameters from the configuration file.  ♦   It is now possible to navigate from the Universal I/O status web page to other web pages.   ♦ Security Update The following security vulnerability has been addressed in this release: CWE-863: Incorrect Authorization The Network-Only user can only perform actions within the Web UI that corresponds to their access level. ♦ ♦ The following security vulnerability has been addressed in this release: CWE-20: Improper Input Validation Incoming BACnet packet sizes are now validated. ♦ ♦   Known Issues   Known Issue There is no known issue in this release.     Hash Signatures   Signatures snst_nmc3_su_3-2-0-8.exe CRC32 C35FC6F7 CRC64 96D9D206CEB88F5C SHA-256 CBEB12D026E980DB7431302A467ACEC8C33E622D18ABE7908A71A9B017A618DE SHA-1 C09CF0C69A1046EC7F15D929599BC536C6DCBB3B BLAKE2sp F7EF95B576FB88C4FB8EE5ECD7FE36C03A18BB05EDD1A19BEC49AC0A8B765DBD   Signatures snst_nmc3_sy_3-2-0-7.exe CRC32 3B9F46E1 CRC64 7AAD51767A944CF3 SHA-256 B147E22EA874C3B72FC40803C565D07143D1EDAFB8D4030A2F4BEF2BB2A19712 SHA-1 8B84CD15549CE397580335C226F6A8A79C07C045 BLAKE2sp B2A29546CE1CB5B5D64060F9C8CA915794BB702E3D643E6B81FDDCC70A0F1C83  
View full article
Lt. Commander SwathiNaidu Lt. Commander
‎2024-10-20 01:14 PM

4933 Views

Release Notes for Smart-UPS & 1-Phase Symmetra Firmware v3.1

Affected Revision Levels   Component  File Details Smart-UPS Application snst_nmc3_su_3-1-1-1-v2.exe UPS Application for Smart-UPS, Smart-UPS RT, Smart-UPS VT, MGE Galaxy 3500. Symmetra Application snst_nmc3_sy_3-1-1-1-v2.exe UPS Application for 1-Phase Symmetra, Symmetra LX.   To upgrade to firmware version 3.0 or later, the only supported method is the Secure NMC System (SNS) Tool, which can be downloaded from www.apc.com/secure-nmc or by searching for SFNMC3FMTSU. To access the firmware in the software, a valid Secure NMC subscription is required. For more information, see the SNS Tool User Guide.   NOTE: If you upgrade to firmware version 2.0 or later, you cannot downgrade to a firmware version lower than 2.0. If you downgrade from firmware version 2.4+ to a firmware version lower than 2.4, this will cause the card to be formatted, erasing all security certificates, encryption keys, configuration settings, and the event and data logs.   New Features   New Feature UPS Family Smart-UPS 1-Phase Symmetra Support added for user authentication via Lightweight Directory Access Protocol (LDAP). ♦  ♦ Support added for baud rate 115,200 on the Console connection on Universal I/O port. ♦ ♦ Support added for optional Spot Fluid Sensor (NBES0301). ♦   Support added for configuring Universal I/O sensors via the cfguio command on the Command Line Interface (CLI). ♦   Support added for remote authentication via the TACACS+ protocol. (Added for Smart-UPS application in v3.0).   ♦ Security Updates Support added for TLS 1.3. ♦ ♦ Support added for SNMPv3 encryption via the SHA-256 and AES-256 protocols. ♦ ♦ Password security has been updated to align with the requirements for IEC 62443-4-2. By default, passwords now need to be a minimum of 8 characters in length (strong password setting enabled). (Added for Smart-UPS application in v3.0)   ♦   Fixed Issues   Fixed Issue UPS Family Smart-UPS 1-Phase Symmetra Link-RX/TX LED is now working for all embedded NMC3s. ♦   Dates in SNMP, such as upsAdvIdentDateOfManufacture, are now available in the correct format, mm/dd/yyyy. ♦   The audit log of the Web UI is displayed in all supported languages. ♦   The NMC3 Web UI now allows passwords with up to 64 characters, as expected. (Added for Smart-UPS application in v3.0)   ♦ For encrypted email settings, install CA certificate to the certificate store and set "Require CA Root Certificate" correctly. (Added for Smart-UPS application in v3.0)   ♦ Improved TLS certificate for email. (Added for Smart-UPS application in v3.0)   ♦ Security Update The following security vulnerability has been addressed in this release: CWE-327: Use of a Broken or Risky Cryptographic Algorithm. This software uses a broken or risky cryptographic algorithm or protocol. Removed support in SSH for diffie-hellman-group14-sha1. ♦ ♦ The following security vulnerability has been addressed in this release: CWE-598: Use of GET Request Method with Sensitive Query Strings. This software uses the HTTP GET method to process a request and includes sensitive information in the query string of that request. Configuration of HSTS is now independent from HTTP or HTTPS configuration. When HSTS is enabled, an STS header is added to all responses over HTTPS. ♦ ♦ The following security vulnerability has been addressed in this release: CWE-307: Improper Restriction of Excessive Authentication Attempts. This software does not implement sufficient measures to prevent multiple failed authentication attempts within a short time frame, making it more susceptible to brute force attacks. The account now gets locked after bad login attempts. ♦ ♦ The following security vulnerabilities have been addressed in this release: CWE-523: Unprotected Transport of Credentials.Login pages do not use adequate measures to protect the user nameand password while they are in transit from the client to the server. CWE-319: Cleartext Transmission of Sensitive Information.The product transmits sensitive or security-critical data in cleartext in acommunication channel that can be sniffed by unauthorized actors. The user is now referred as an index rather than the user name NMC/KrtUvuh39YtQmHbyua297g/usercfg.htm?user=2. ♦ ♦ The following security vulnerability has been addressed in this release: CWE-200: Exposure of Sensitive Information to An Unauthorized Actor SSH Cipher Block Chaining (CBC) cipher has been removed. ♦ ♦ The following security vulnerabilities have been addressed in this release: CWE-74: Improper neutralization of special elements in output used bya downstream component (Injection) CWE-79: Improper neutralization of input during web page generation (Cross-site Scripting). (Added for Smart-UPS application in v3.0)   ♦   Known Issues   Known Issue There is no known issue in this release.     Hash Signatures   Signatures snst_nmc3_su_3-1-1-1-v2.exe CRC32 51F99D98 CRC64 0E8E079EEEEB03FF SHA-256 55E762F6D3E8CF751527A30D109A730E5029BFED261A2D3AE4D645D2FFA0EA1F SHA-1 D6D4181A620C0606863C6F808774F9C3E773F70D BLAKE2sp 80A283A939A16A48ED554002F2E284AB862685370B2EDEF6FF51BF0232C65AB0     Signatures snst_nmc3_sy_3-1-1-1-v2.exe CRC32 63A316A1 CRC64 9B16BD59FB4FAA58 SHA-256 C9C2BA0E8CC0FFE7DE1716817E5AD74F19B46B8D80569F3E402BBA3D6A3FB6D7 SHA-1 929DFB72C2A94D71C2A0938FD0A675ABE8BAC4E9 BLAKE2sp BCD8B84A96027231279FDC88B20363F2384DAF55D2C99E7A3F62B9DB3ABB4FB1    
View full article
Lt. Commander SwathiNaidu Lt. Commander
‎2024-10-20 12:49 PM

3435 Views

Release Notes for Smart-UPS v2.5.3.3 & 1-Phase Symmetra Firmware v2.5.3.2

Affected Revision Levels   Component  File Details Smart-UPS Application apc_hw21_su_2-5-3-3.nmc3 UPS Application for Smart-UPS, Smart-UPS RT, Smart-UPS VT, MGE Galaxy 3500. Symmetra Application apc_hw21_sy_2-5-3-2.nmc3 UPS Application for 1-Phase Symmetra, Symmetra LX.   For details on upgrading the UPS Network Management Card 3 (NMC 3) firmware, see the NMC3 User Guide. NOTE: If you upgrade to firmware version 2.0 or later, you cannot downgrade to a firmware version lower than 2.0.     If you downgrade from firmware version 2.4+ or later to a firmware version lower than 2.4, this will cause the card to be formatted, erasing all security certificates, encryption keys, configuration settings, and the event and data logs.   New Features   New Feature There is no new feature in this release.   Fixed Issues   Fixed Issue UPS Family Smart-UPS 1-Phase Symmetra Downloading the Event Log via the Web UI works as expected when the language is set to Japanese. ♦ ♦   Security Update   The following security vulnerability has been addressed in this release:  CWE-200: Exposure of Sensitive Information to an Unauthorized Actor SSH Cipher Block Chaining (CBC) cipher has been removed. ♦ ♦ The following security vulnerabilities have been addressed in this release: CWE-523: Unprotected Transport of Credentials. Login pages do not use adequate measures to protect the user name and password while they are in transit from the client to the server. CWE-319: Cleartext Transmission of Sensitive Information. The product transmits sensitive or security-critical data in cleartext in a communication channel that can be sniffed by unauthorized actors. The user is now referenced as an index rather than their username, for example: NMC/KrtUvuh39YtQmHbyua297g/usercfg.htm?user=2 ♦ ♦ The following security vulnerability has been addressed in this release:   CWE-863: Incorrect Authorization The Network-Only user can only perform actions in the Web UI relevant to the user access level. ♦ ♦ The following security vulnerability has been addressed in this release: CWE-20: Improper Input Validation Incoming BACnet packet sizes are now validated. ♦ ♦ The following security vulnerability has been addressed in this release: CWE-598: Use of GET Request Method With Sensitive Query Strings. This software uses the HTTP GET method to process a request and includes sensitive information in the query string of that request. Configuration of HSTS is now independent from HTTP or HTTPS configuration. When HSTS is enabled an STS header is added to all responses over HTTPS. ♦ ♦   Known Issues   Known Issue There is no known issue in this release.   Hash Signatures Signatures apc_hw21_su_2-5-3-3.exe  CRC32 1B525C68 CRC64 1919EC007B13BC96 SHA-256 C641E5D549CB88F6CDF914A9BD79A3F450118FC9CE6ADA47EA35A5C96FFA77C1 SHA-1 BCF0BE585DD3E21AF7A3ADA8F7893B5A0B8F1198 BLAKE2sp 6DBF86236F9B6EE639B42A883F832182ADF9990D99801ECD5FA4B8D1E42F56FA   Signatures apc_hw21_sy_2-5-3-2.exe CRC32 04E90885 CRC64 20EA59213CDCA39E SHA-256 091163C905F29652AB41B4ABE12CA45402376B6CACD80E5911C9DDB2CC308134 SHA-1 FCFB7578356DFC98253BDDCBA2C483AF76DF8A43 BLAKE2sp 50CC9F255DE9DF12FB94C3AAD92661500CBB05FEB4A5DEF8BCDF1691529D4736  
View full article
Lt. Commander SwathiNaidu Lt. Commander
‎2024-11-15 09:48 AM

3412 Views

Release Notes for Smart-UPS Firmware v3.0.0.12

Affected Revision Levels   Component  File Details Smart-UPS Application apc_hw21_su_3-0-0-12.nmc3 UPS Application for Smart-UPS, Smart-UPS RT, Smart-UPS VT, and MGE Galaxy 3500.     To upgrade to firmware version 3.0 or later, the only supported method is the Secure NMC System (SNS) Tool, which can be downloaded from www.apc.com/secure-nmc or by searching for SFNMC3FMTSU. To access the firmware in the software, a valid Secure NMC subscription is required. For more information, see the SNS Tool User Guide. NOTE: If you upgrade to firmware version 2.0 or later, you cannot downgrade to a firmware version lower than 2.0.   If you downgrade from firmware version 2.4+ to a firmware version lower than 2.4, this will cause the card to be formatted, erasing all security certificates, encryption keys, configuration settings, and the event and data logs.   Schneider Electric Device IP Configuration Wizard  The Device IP Configuration Wizard is a Windows application designed specifically to remotely configure the basic TCP/IP settings of Network Management Cards. The Wizard runs on Windows® Server 2012, Windows Server 2016, Windows Server 2019, Windows 8.1, and Windows 10. This utility is for IPv4 only. NOTES: In firmware version v1.4.x and higher, it is not supported to assign IP addresses to Network Management Cards using the Wizard. You cannot search for assigned devices already on the network using an IP range unless you enableSNMPv1 and set the Community Name to “public”. For more information on SNMPv1, see the User Guide. When the NMC IP address settings are configured, to access the NMC Web UI in a browser, you must update the URL from http to https.   New Features   New Feature The NMC3 platform and Smart-UPS application are now IEC 62443-4-2 certified. Support has been added for audit logging to ensure control actions and configuration changes are recorded in the Event log. Support has been added for remote authentication via the TACACS+ protocol. Security Update Password security has been updated to align with the requirements for IEC 62443-4-2.The NMC now supports UPS firmware updates while the UPS is in Manual Bypass mode.     Fixed Issues   Fixed Issue SNMP OID upshighprecbatterypackonly now correctly displays all information about Battery Packs. The NMC3 Web UI now allows passwords with up to 64 characters, as expected. For encrypted email settings, install CA certificate in the certificate store and set "Require CA Root Certificate" correctly. Improved TLS certificate for email. Security Update The following security vulnerabilities has been addressed in this release: CWE-74: Improper neutralization of special elements in output used by a downstream component (injection) CWE-79: Improper neutralization of input during web page generation (Cross-site Scripting).   Known Issues   Known Issue The audit log of the Web UI is currently only available in English.     Hash Signatures   Signatures snst_nmc3_su_3-0-0-12.exe CRC32 CED0ED3C CRC64 0561C9C18A9E643C SHA-256 EB5245DFC880F7A8F4FA17484347FA9E0E4BE7EF1FD7E7C6FDA441A268E084D2 SHA-1 A7A7197534FD0FD4F6D8950ACFB6537F59D69FCC BLAKE2sp B33E36481699B0A7B5A029E78EC47914C5D0192614B79C794EE399689C7CE4D9
View full article
Lt. Commander SwathiNaidu Lt. Commander
‎2024-06-19 03:55 AM

Last Updated: Commander CDiggin Commander ‎2024-06-25 06:40 AM

2885 Views

Release Notes for Smart-UPS & 1-Phase Symmetra Firmware v3.3.0.8

    Affected Revision Levels   Component  File Details Smart-UPS Application Windows: snst_nmc3_su_3-3-0-8.exe Linux & macOS:  snst_nmc3_su_3-3-0-8.tar.gz UPS Application for Smart-UPS, Smart-UPS RT, Smart-UPS VT, MGE Galaxy 3500. Symmetra Application Windows:  snst_nmc3_sy_3-3-0-8.exe Linux & macOS:  snst_nmc3_sy_3-3-0-8.tar.gz   UPS Application for 1-Phase Symmetra, Symmetra LX.   To upgrade to firmware version 3.0 or later, the only supported method is the Secure NMC System (SNS) Tool, which can be downloaded from www.se.com/secure-nmc or by searching for SFNMC3FMTSU. To access the firmware in the software, a valid Secure NMC subscription is required. For more information, see the SNS Tool User Guide.   NOTE: If you upgrade to firmware version 2.0 or later, you cannot downgrade to a firmware version lower than 2.0.   If you downgrade from firmware version 2.4+ to a firmware version lower than 2.4, this will cause the card to be formatted, erasing all security certificates, encryption keys, configuration settings, and the event and data logs.   New Features   New Feature UPS Family Smart-UPS 1-Phase Symmetra The NMC3 platform and Smart-UPS and 1-Phase Symmetra applications are now IEC 62443-4-2 SL2 certified; a higher level of certification than SL1 announced in October 2023. ♦ ♦ Command Line Interface (CLI) added to the Web UI under Control > Network > Web CLI. ♦ ♦   Fixed Issues   Fixed Issue UPS Family Smart-UPS 1-Phase Symmetra The LDAP TLS connection now works as expected when connecting to an IP address and server certificate using SAN type "iPAddress".    ♦ ♦ DHCPv6 no longer intermittently reboots when the network interface starts or when the Ethernet cable is reseated. ♦  ♦ Improved logging for account disabled events. ♦  ♦ The expiration date of self-signed certificates has been updated.  ♦ ♦ You can now send emails as expected if the SMTP server uses an IPv6 address.    ♦  ♦ The severity of Syslog-related events in the configuration file has been corrected. ♦  ♦ SmartSlot NMC, with NTP enabled and a non-zero IPv4 address, is now allowed to set the UPS Last Battery Replacement Date when the embedded NMC does not have a network connection. ♦   For UPS devices that do not have a valid serial number on their internal battery modules, the NMC will no longer show the serial number on the Web UI. ♦     Security Update   The following third-party components (open source or proprietary) have been updated to address cybersecurity vulnerabilities:  RADIUS Protocol under RFC 2865 - CVE-2024-3596 Implemented support for the Message-Authenticator attribute. ♦  ♦ The following security vulnerability has been addressed in this release:  CWE-1285: Improper Validation of Specified Index, Position, or Offset in Input Fixed an improper user input validation. ♦  ♦   Known Issues   Known Issue There is no known issue in this release.   Hash Signatures   Windows Signatures snst_nmc3_su_3-3-0-8.exe CRC32 29F3F0A9 CRC64 27EECC865F1F2EC9 SHA-256 D625F26E44E0385A109079432D6F692871CE5FA962378C222159AC5334F1CD56 SHA-1 17FAEA0C8235B90BE52C27FA9E30A9390FDB83B6 BLAKE2sp DF8183FFE1BA8D6418256FF3562991C2BFA80B3EBE7317DD65B4D5833375BA42   Signatures snst_nmc3_sy_3-3-0-8.exe CRC32 8717AA00 CRC64 57CB1061F06F8C6B SHA-256 A14F2D57C6822B0364525E19A1A8F764F4C03B44F3CB10631332B7665C2368A8 SHA-1 98683E86EAD544414A922597000598B21011B47D BLAKE2sp E6112CF93A7B80F65259881525C26F5E54C24D8F8A50E582064EE5A13EAAE455   Linux Signatures snst_nmc3_su_3-3-0-8.tar.gz CRC32 F9255B7B CRC64 C99BACD067E0850C SHA-256 09A68FD73E62959CB472178348D09FB01C58A0924F5321FD2C5634DF0B18140D SHA-1 AB242A6FBB4A8F6271861F3E18AD45AAA1A19548 BLAKE2sp CF8FF92739BCD7F36094F1A6BB1503DEF2F1654883A791796A52D2F921FA9C18   Signatures snst_nmc3_sy_3-3-0-8.tar.gz CRC32 85192DE2 CRC64 4C5A84642CFF86E5 SHA-256 B074B8FC98B80B552CBFD1A4AA27FEDAF32AE2EE96E7E35DE840CEC63000AF62 SHA-1 2F95AB8AB3E085829E27F61859276C2A4317B0D9 BLAKE2sp 8598726B3D8048CB78D3A3DA3820765EE2A42B35AA3A3181B26FA8BB8AB36A94     macOS Signatures snst_nmc3_su_3-3-0-8.tar.gz CRC32 AD6684B4 CRC64 3D3BDE289D776A84 SHA-256 A37C5F80E5189748294D667A7125C139778D7C026B64E3662BA6A109C4F73BDF SHA-1 863AA7F1866B7CBC12D77E34ADACA54C7590FC1A BLAKE2sp 47C036DBEA9FCFF831683AE603487C73431C902FA44510F4D8CA3D50A22DC781   Signatures snst_nmc3_sy_3-3-0-8.tar.gz CRC32 3824F216 CRC64 86B354CD79925D05 SHA-256 B572975C0CF17817335033D4BF98562D96D53E9DBE96F4D92F695928E4C3C082 SHA-1 8D927310FB0D4C6A29BF38885954656A65770BD1 BLAKE2sp 9C4FFB105C93F9E589E8AE4E817465B560A5A387A88F22D625ADD8F3D06AEE9E
View full article
Lt. Commander SwathiNaidu Lt. Commander
‎2025-03-03 12:07 AM

1812 Views

Release Notes for Smart-UPS v2.5.4 & 1-Phase Symmetra Firmware v2.5.4

Affected Revision Levels   Component  File Details Smart-UPS Application apc_hw21_su_2-5-4-4.nmc3 UPS Application for Smart-UPS, Smart-UPS RT, Smart-UPS VT, MGE Galaxy 3500. Symmetra Application apc_hw21_sy_2-5-4-4.nmc3 UPS Application for 1-Phase Symmetra, Symmetra LX.   For details on upgrading the UPS Network Management Card 3 (NMC 3) firmware, see the NMC3 User Guide. NOTE: If you upgrade to firmware version 2.0 or later, you cannot downgrade to a firmware version lower than 2.0.     If you downgrade from firmware version 2.4+ or later to a firmware version lower than 2.4, this will cause the card to be formatted, erasing all security certificates, encryption keys, configuration settings, and the event and data logs.   New Features   New Feature There is no new feature in this release.   Fixed Issues   Fixed Issue UPS Family Smart-UPS 1-Phase Symmetra DHCPv6 no longer intermittently reboots when the network interface starts or when the Ethernet cable is reseated. ♦ ♦ You can now send emails as expected if the SMTP server uses an IPv6 address.   ♦ ♦   Security Update   The following security vulnerability has been addressed in this release: CWE-200: Exposure of Sensitive Information to an Unauthorized Actor SSH Cipher Block Chaining (CBC) cipher has been removed. ♦ ♦ The following third-party components (open source or proprietary) have been updated to address cybersecurity vulnerabilities: RADIUS Protocol under RFC 2865 - CVE-2024-3596 Implemented support for the Message-Authenticator attribute. ♦  ♦   Known Issues   Known Issue There is no known issue in this release.   Hash Signatures Signatures apc_hw21_su_2-5-4-4.exe CRC32 ABD1E96D CRC64 4BFC3228E57AEA20 SHA-256 1720FFF38427A23DEC4FFF20F3D295E85A17EA5CCF6888778B9B7B89361B73A7 SHA-1 1D7C7AC33EE8C5F0D0EBEBA9925FC1D29E258DD2 BLAKE2sp 155406516024C84132F449E6F5F6563EF4B9FF5CA60D2CFD0219FFC10F9C670C   Signatures apc_hw21_sy_2-5-4-4.exe CRC32 2FFEA4BA CRC64 180E8F764B36BE4B SHA-256 FDBD6CEF4BD060B094A9916BDA38EE3181215C013258959988CEC776D8EFE5BB SHA-1 9046F72622DBE82B8A4D9E2F2816DD06584A186B BLAKE2sp E1ECA538E02D9EF0247112330F6BC8C1FB8DAED8B6A342E94E06B64F3B43DF43  
View full article
Lt. Commander SwathiNaidu Lt. Commander
‎2025-03-11 10:15 AM

878 Views

Release Notes for Smart-UPS v2.5.5.1

Affected Revision Levels   Component  File Details Smart-UPS Application apc_hw21_su_2-5-5-1.nmc3 UPS Application for Smart-UPS, Smart-UPS RT, Smart-UPS VT, MGE Galaxy 3500.   For details on upgrading the UPS Network Management Card 3 (NMC 3) firmware, see the NMC3 User Guide. NOTE: If you upgrade to firmware version 2.0 or later, you cannot downgrade to a firmware version lower than 2.0.     If you downgrade from firmware version 2.4+ or later to a firmware version lower than 2.4, this will cause the card to be formatted, erasing all security certificates, encryption keys, configuration settings, and the event and data logs. New Features   New Feature There is no new feature in this release.   Fixed Issues     Fixed Issue Database corruption during power failures or restarts while writing data is now resolved.   Known Issues   Known Issue There is no known issue in this release.   Hash Signatures   Signatures apc_hw21_su_2-5-5-1.exe CRC32 B8D94E3C CRC64 1783A0689216503A SHA-256 4F26317441B96A768F06DC03F93C52714F51D78D8911E670034C371EDEB1C15A SHA-1 18913F6D0FDE2BE3DB5F9E0786BA5693D1E05FB6 BLAKE2sp C8CE7DC6D56CBB6FE680E9AEAA9DA8587DD7DFDCB66409E86874F2F3B7B4B46A  
View full article
Lt. Commander SwathiNaidu Lt. Commander
‎2025-06-17 10:04 AM

575 Views

Release Notes for Smart-UPS & 1-Phase Symmetra Firmware v3.4.0.8

  Affected Revision Levels   Component  File Details Smart-UPS Application Windows: snst_nmc3_su_3-4-0-8.exe Linux & macOS:  snst_nmc3_su_3-4-0-8.tar.gz UPS Application for Smart-UPS, Smart-UPS RT, Smart-UPS VT, MGE Galaxy 3500. Symmetra Application Windows:  snst_nmc3_sy_3-4-0-8.exe Linux & macOS:  snst_nmc3_sy_3-4-0-8.tar.gz   UPS Application for 1-Phase Symmetra, Symmetra LX.   To upgrade to firmware version 3.0 or later, the only supported method is the Secure NMC System (SNS) Tool, which can be downloaded from www.se.com/secure-nmc or by searching for SFNMC3FMTSU. To access the firmware in the software, a valid Secure NMC subscription is required. For more information, see the SNS Tool User Guide.   NOTE: If you upgrade to firmware version 2.0 or later, you cannot downgrade to a firmware version lower than 2.0.   If you downgrade from firmware version 2.4+ to a firmware version lower than 2.4, this will cause the card to be formatted, erasing all security certificates, encryption keys, configuration settings, and the event and data logs.   New Features   New Feature UPS Family Smart-UPS 1-Phase Symmetra Support added for viewing the ARP cache in the Command Line Interface (CLI). ♦ ♦ Support added for EtherNet/IP for selected UPS devices. For more information, refer to Knowledge Base article FAQ000275863.  ♦   NMC now displays the UPS Installation date when supported by the UPS. ♦   Added support for configuring outlet groups from the Command Line Interface. ♦   Security Update Support added for Multi-Factor Authentication (MFA). MFA adds an additional layer of security to user logins by requiring a one-time password (OTP) sent via email after successful username and password authentication.  NOTE: Ensure the NMC user credentials used for the SNS Tool, EcoStruxure IT and Data Center Expert communications do not have email addresses configured. For more information, see Knowledge Base article FAQ000276382. ♦ ♦   Fixed Issues   Fixed Issue UPS Family Smart-UPS 1-Phase Symmetra Unsuccessful e-mail tests are now displayed as expected in the Web UI.  ♦ ♦ Styling for the “Password Change Required” web page now displays as expected in the latest update of Chrome.   ♦  ♦ You can now cancel an initiated firewall test as expected in the Web UI.  ♦  ♦ CIDR (Classless Inter-Domain Routing) notation is now allowed in SNMP NMS fields and firewall fields (when in subnet mode).    ♦ ♦ The CIDR notation is now functional in the DNS field and NMP access is now allowed or blocked based on the ranges associated with the network.   ♦  ♦ DNS lookups previously returned unusable IPv6 addresses in certain scenarios when both IPv4 and IPv6 were enabled (default settings). IPv4 is now prioritized if the NMC has an IPv4 address and only a link-local IPv6 address.  ♦  ♦ The NMC now shows the correct RBC SKU string for battery replacement. ♦   The NMC now properly supports USB flash drives for accessing configuration options via the UPS display. ♦     Security Update   The following security vulnerability has been addressed in this release: CWE-120: Buffer Copy without Checking Size of Input vulnerability exists that could cause the device to become unresponsive when malformed SNMP requests are received over the network.  ♦ ♦ The following security vulnerability has been addressed in this release: CWE-476: NULL Pointer Dereference vulnerability exists that could cause the device to become temporarily inaccessible when receiving malformed IPv4 packets. ♦ ♦ The following security vulnerability has been addressed in this release: CWE-613: Insufficient Session Expiration vulnerability exists that could cause a user to maintain access to an existing session when their password has been changed.  ♦ ♦   Known Issues   Known Issue There is no known issue in this release.   Hash Signatures   Windows Signatures snst_nmc3_su_3-4-0-8.exe CRC32 45B34E48 CRC64 D073654FF833808B SHA-256 35B2DE418E22D5241CB36A94C15FEBAF49E6AA46E90FA84BE685CBC4218EC70C SHA-1 BAF4343761DB6D3DA916ECA5836A1F0131653F81 BLAKE2sp E53287ED5744059A72F1BC59A911082E09B8548E2F4EA01F9A34FB796F362FEE   Signatures snst_nmc3_sy_3-4-0-8.exe CRC32 F3BF4CCF CRC64 907C7F8101C41264 SHA-256 4A84BB6DBE87313FBF9F751118EE0BE3036749713E87A61AFCEED92FCDCDB802 SHA-1 7D2451F2CC1B2E4FA5E34DB3EF342204268FADB4 BLAKE2sp DBE7CDEF8B615F592E8E5E3EB531DC7ED166C5A78B8B01164C6016838BDE21EA   Linux Signatures snst_nmc3_su_3-4-0-8.tar.gz CRC32 F4C123A8 CRC64 002F814120317B02 SHA-256 66CE945D8D13811760DF1E249C51B492415F62DDBD8A329E4FFF3F8F14AD14C8 SHA-1 242548A1D794AB86D8B31527FFB1C9025A2DF5A9 BLAKE2sp 4E9F592B433E6E467B964231D70E19829B6B19955DED67B185F33AFBE7926A62   Windows Signatures snst_nmc3_sy_3-4-0-8.tar.gz CRC32 316540EB CRC64 AE3E7B930CA360D9 SHA-256 272EF5CE98C18C3AA9E8D822799C77B4194F36808F4FAF5F0075BF15A9092B00 SHA-1 88A7B68E9791FFFC8ABA11F1ADF90AE192B01293 BLAKE2sp A903D65FE11A55F38F62D50A9C42742B42436407EF9B87A63037D958181F72E6       macOS Signatures snst_nmc3_su_3-4-0-8.tar.gz CRC32 DC9E7DE1 CRC64 D24D77554F730E68 SHA-256 0B5562C2A883AA31EA105F90FB2E7AEBDFADA314418051ABC6F8DBA737F62111 SHA-1 6DCF6023F9A70FFF7710F91B425F5908C1D5D2A3 BLAKE2sp 93731344D22790B9080573089A7F8F41A3071BB5F3A30D09C028068A6A9E8D6B   Signatures snst_nmc3_sy_3-4-0-8.tar.gz CRC32 64EAFB15 CRC64 2B47491CD052BDCA SHA-256 0634E006909A90B4EA1A6F2B7656324E63295AD2D3F9247D67C9E23ED548BBA4 SHA-1 DC266F489C01758913375596211CFEE2955206F0 BLAKE2sp 62CB4EAE53E5B6390E5EB56FF857536D7EC91D2AAE169437F0D044B06FC03BE9
View full article
Lt. Commander SwathiNaidu Lt. Commander
‎2025-08-26 03:32 AM

412 Views

Release Notes for Smart-UPS & 1-Phase Symmetra Firmware v3.4.1.1

Affected Revision Levels   Component  File Details Smart-UPS Application Windows: snst_nmc3_su_3-4-1-1.exe Linux & macOS:  snst_nmc3_su_3-4-1-1.tar.gz UPS Application for Smart-UPS, Smart-UPS RT, Smart-UPS VT, MGE Galaxy 3500. Symmetra Application Windows:  snst_nmc3_sy_3-4-1-1.exe Linux & macOS:  snst_nmc3_sy_3-4-1-1.tar.gz   UPS Application for 1-Phase Symmetra, Symmetra LX.   To upgrade to firmware version 3.0 or later, the only supported method is the Secure NMC System (SNS) Tool, which can be downloaded from www.se.com/secure-nmc or by searching for SFNMC3FMTSU. To access the firmware in the software, a valid Secure NMC subscription is required. For more information, see the SNS Tool User Guide.   NOTE: If you upgrade to firmware version 2.0 or later, you cannot downgrade to a firmware version lower than 2.0. If you downgrade from firmware version 2.4+ to a firmware version lower than 2.4, this will cause the card to be formatted, erasing all security certificates, encryption keys, configuration settings, and the event and data logs.   New Features   New Feature There is no new feature introduced in this release.       Fixed Issues   Fixed Issue UPS Family Smart-UPS 1-Phase Symmetra There is no fixed issue in this release.   Security Update   The following security vulnerabilities have been addressed in this release: CWE-1286: Improper Validation of Syntactic Correctness of Input CWE-787: Out-of-bounds Write CWE-120: Buffer Copy without Checking Size of Input ♦ ♦   Known Issues   Known Issue There is no known issue in this release.   Hash Signatures   Windows Signatures snst_nmc3_su_3-4-1-1.exe CRC32 9BF123A4 CRC64 C669A75A2C817482 SHA-256 8E2759312DFBA7C26190E7001C6279E57545BEA57660B913C5F7E9885171A292 SHA-1 73DFDB117F515BF59D2AC8495FFE952FEF3CB84C BLAKE2sp 0EEBADD9C215B3736637C7940C5F39A1F01FAE4500E07CA2E982E28FCD8108FB   Signatures snst_nmc3_sy_3-4-1-1.exe CRC32 DF39BBF1 CRC64 DC13FDD223797FE5 SHA-256 794AA6DE55703D1BB3C6F6DB4EFDD79B415DDB64CE04B2DE8A20E17C7246DAA0 SHA-1 7A5EE03E7D2319CF87B9D4525110999F28EA7227 BLAKE2sp 8E72B8BAAD166A28C434490D929A51BCEC6C5E3E288EEEA8597CD39F27F67703     Linux Signatures snst_nmc3_su_3-4-1-1.tar.gz CRC32 EAC2C08E CRC64 8E8300555DA354E7 SHA-256 8D4ED8ACF570905355247877E68E723F192998EECE0383998F0B7F9D5C592927 SHA-1 856437E4DD4CA8E6CAD7B4664A6D31D99E57FD4F BLAKE2sp F2458EBADC7C38CA878D739DE42E10A9E3596B0D3633C5FC40945C52BA536B66   Signatures snst_nmc3_sy_3-4-1-1.tar.gz CRC32 8C8EE922 CRC64 CD12C071A6CBBFEE SHA-256 8687C5BEC7F5D986042B25C785CBD6A75FD5319186353AB3FE8D26177E2C8B54 SHA-1 0373EF84EDF489EF573604C8EBF11A8658E903B7 BLAKE2sp 9B146B7C1E473A63F55CC225B6A5393AEA6E7E8BD410487CB366D2A17008C39C     macOS Signatures snst_nmc3_su_3-4-1-1.tar.gz CRC32 B40200AD CRC64 2FA8CA63567EEB93 SHA-256 6DAB706D58F14CEA4CE41A353CBE4E272B3E399CC748F27AC91C58D17E705DCA SHA-1 21A31CDBA204C448E456235C4E3C39ED2EEE2CFB BLAKE2sp 08C46256114F27F7EF2FD8C95A812C86697AA97467561039D9E71C12FA7FF710   Signatures snst_nmc3_sy_3-4-1-1.tar.gz CRC32 EC9BF516 CRC64 0845A674E1A81E2A SHA-256 5A2A73D0EEB26B8B15DBCE74B46A55976782151AA6A486AEDE9DF060A9413DC4 SHA-1 293C5525FB2450463111C95A900FBE12525D68AD BLAKE2sp 9C1C4521B8CBBB0254C5C9E4CAC66989ECEBF16FC4413F74B9E192299C053520
View full article
Lt. Commander SwathiNaidu Lt. Commander
‎2025-12-01 11:53 PM

on ‎2025-12-01 11:53 PM

149 Views
Didn't find what you are looking for? Ask our Experts
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore