Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

True RMS current for neutral

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Re: True RMS current for neutral
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
488
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
89
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Metering & Power Quality
EvonneYin
Ensign EvonneYin Ensign
Ensign

Posted: ‎2013-12-11 03:13 PM

0 Likes
4
1227
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-12-11 03:13 PM

True RMS current for neutral

Hi All,

I hope anyone of you could help me on this one. Does ION7300 have true RMS current for neutral reading?

I found an information which shows I4-residual current calculation as current flow in the neutral.

Is it calculated and not true RMS reading?

Please advise.

Regards,

Evonne

Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Anonymous user
Not applicable

Posted: ‎2013-12-18 10:21 PM

0 Likes
1
1164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-12-18 10:21 PM

Hi Evonne,

Not sure whether you have found the answer to your question by other means.

Anyway, the ION73xx series does not have I4 current input hence it is not true RMS measurement. The next model up ION7550 & ION7650 have I4 and I5 input for CTs.

Regards

Ed

Reply
JamesAZZO
Sisko | EcoXpert Master JamesAZZO Sisko | EcoXpert Master
Sisko | EcoXpert Master

Posted: ‎2013-12-19 12:09 AM

0 Likes
0
1164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-12-19 12:09 AM

As do the new PM556x meters...

Reply
Anonymous user
Not applicable

Posted: ‎2013-12-19 11:17 AM

0 Likes
1
1164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-12-19 11:17 AM

 

"true RMS" is generally accepted to indicate a measurement for any waveshape that is proportional to heat dissipated by a resistive load attached to this signal (as opposed to assuming the signal is sinusoidal).

The 7300 series does not have a physical I4 terminal so it (obviously) is a derived quantity. Derived does not mean that it is or is not true rms, but in the case of the 73xx I4 is a vector summation of fundamental phase currents (so not true RMS).

The PM8000 and 86xx do compute true RMS of a derived residual current. The 75/7650 series has additional terminals to make real measurements.

Reply
engineer_langfo
Lieutenant JG engineer_langfo
Lieutenant JG

Posted: ‎2016-02-01 01:31 PM

0 Likes
0
1164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-02-01 01:31 PM

One side note: the ION8650 series does not calculate I4 (residual current).   This value (for whatever reason) is missing in the ION8650.

The inputs of the ION7550/7650 will return a 0 if there is no CT in the I4. 

Besrat gave me this great equation to calculate residual current which is only valid for ION OS meters with Power Harmonics Module.  Apparently it is in a KB article, and referenced elsewhere, but I cannot seem to find...

___________________________________________________________________________

- Create a Power Harmonics Module

- In setup registers set the harmonic number to 1 (the fundamental)

- Create arithmetic that acquires values for I1, I2 and I3 magnitude and phase from the PHM above.

- using the arithmetic, decompose these signals into rectangular components with:

Inx = |In|*cos(angleIn)

Iny = |In|*sin(angleIn)

for each phase.

- now seperately add the x and y components of each phase giving a total x and y.

I4x = I1x + I2x + I3x

I4y = I1y + I2y + I3y

- using an arithmetic, find the magnitude of the fundamental I4 with:

|I4| = sqrt((I4x)^2 + (I4y)^2)

Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of