Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Important Announcement: Community Back to Full Functionality

Dear Members, we are thrilled to announce that our Community is back to full functionality and that posts publication is now enabled again! We appreciate your patience during the last weeks. Learn more about our Community Guidelines. Thank you, Schneider Electric Community Team.

The timing of NTP synchronization of the ION meters.

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • The timing of NTP synchronization of the ION meters.
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
299
Ramasamy_N
Commander Ramasamy_N Commander
75
DanL
Captain DanL Captain
72
Robert_Lee
Captain Robert_Lee Captain
67
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Tomohiro-Okada
Lieutenant JG Tomohiro-Okada
Lieutenant JG

Posted: ‎2022-06-30 01:32 AM

0 Likes
7
1228
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-30 01:32 AM

The timing of NTP synchronization of the ION meters.

Hi 

 

I have two questions about time synchronization of ION9000.

 

I did time synchronization settings of the ION9000 meter(sync with NTP server via Ethernet.)

and the time synchronization worked well.

 

The meter settings are below.

 

Metering Setup - Nameplate Info
FAC1 DeviceType 9000
FAC1 Revision 003.001.000
FAC1 Feature Set Standard

FAC1 Template 9000_V3.1.0.0.0

 

Advanced Ethernet - NTP
CL1 Enable NTP Time Sync NTP
CL1 NTP Time Sync Interval 1 day
CL1 Event Logging Threshold 0.02
ETH1 NTP Server 192.168.000.010
CL1 Time Sync Type UTC
CL1 Time Sync Source ETHERNET

 

but  only the cycle of the time sync looked random.

(In spite of the "NTP Time Sync Interval" setting was "1day",

 the Event history of the synchronization  with NTP server was  roughly about every hour.

About 20 times time synchronization was done in a day.)

 

Why was this happened?

 

The second question is the timing of the time synchronization.

 

For example, If I set the  "NTP Time Sync Interval"  setting to "1day" and the first time sync was 2022/06/30 09:00.

The next time sync will be 2022/07/01 09:00 I think.

But, the event history of the time sync was not so.

What factors decide the timing?

and can I define the timing of the synchronization?

 

Regards,

Okada

 

 

 

 

 

Labels
  • Labels:
  • ION9000
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2022-07-04 10:12 AM

0 Likes
3
1113
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-04 10:12 AM

Hello @Tomohiro-Okada ,

 

If the meter is set to SNTP, each time packet received by the meter should contain specific information, What time the meter sent the SNTP request, what time the NTP server got the request and what time NTP server sent the response. The meter would calculate the delta or transit time based on these three pieces of information as as well the local time on the meter when the packet was received by the meter. Based on this delta calculation and the SNTP/NTP servers' timestamps, the clock on the meter is adjusted.

 

NTP is significantly more complex. NTP uses complex statistical algorithms, aimed at filtering small discrepancies. NTP is intended to adjust the 'tick' rate of the device 'what is the length of a second' rather than just adjusting the clock time every x seconds. There are multiple variables that go into the calculations to determine how much to adjust a second. From time to time there may need to be a time step event to help the meter's clock adjust to match the NTP server's time. If this jump is greater than the threshold you will see the event in meter's event log, "time about to change" and "time change". Looking at the time stamp of these events you can calculate the approximate adjustment of the meter's clock.

 

"how long does the quartz crystal unit of the ION9000 or PM8000 can work correctly?" I am not 100% sure I understand the question. If you are asking what is the expected lifetime of the crystal, this will match or exceed the expected life time of the meter. Or if you are asking if okay to keep using the internal crystal, the answer is yes, this is okay.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 7
DanL
Captain DanL Captain
Captain

Posted: ‎2022-06-30 09:40 AM

1 Like
6
1203
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-30 09:40 AM

The unfortunately named "CL1 NTP Time Sync Interval" can only configure SNTP time sync intervals (not NTP).

Be sure to configure the "CL1 Clock Source" to "Internal" ("COMM" is also acceptable as with NTP enabled it will behave as "Internal"). Never use an external time sync source with the Clock Source configured to "Line Freq".

 

If you continue to have issues, please contact support for additional troubleshooting steps

Tags (1)
  • Tags:
  • english
Reply
Tomohiro-Okada
Lieutenant JG Tomohiro-Okada
Lieutenant JG

Posted: ‎2022-07-01 12:32 AM

0 Likes
5
1186
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-01 12:32 AM

Hi @DanL 

 

Thank you for your reply.

 

So if the protocol is "NTP"(not "SNTP"), is the timing of the time sync random?

 

And if I change  the  "CL1 Clock Source" setting to "Internal", how long does the quartz crystal unit of the ION9000 or PM8000

can work correctly?

 

I'd like to know the product lifetime of the quartz crystal unit.

 

Regards,

Okada

 

 

 

Tags (1)
  • Tags:
  • english
Reply
Tomohiro-Okada
Lieutenant JG Tomohiro-Okada
Lieutenant JG

Posted: ‎2022-07-01 12:53 AM

0 Likes
4
1182
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-01 12:53 AM

Hi @DanL,

 

I have one more question.

 

If the protocol is "NTP"(not "SNTP"), does the gap of the time between PQM and NTP server affects time sync interval?

What factors decide the execution timing of the time sync when the protocol is "NTP"(not SNTP)?

 

Thanks,

Okada

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2022-07-04 10:12 AM

0 Likes
3
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-04 10:12 AM

Hello @Tomohiro-Okada ,

 

If the meter is set to SNTP, each time packet received by the meter should contain specific information, What time the meter sent the SNTP request, what time the NTP server got the request and what time NTP server sent the response. The meter would calculate the delta or transit time based on these three pieces of information as as well the local time on the meter when the packet was received by the meter. Based on this delta calculation and the SNTP/NTP servers' timestamps, the clock on the meter is adjusted.

 

NTP is significantly more complex. NTP uses complex statistical algorithms, aimed at filtering small discrepancies. NTP is intended to adjust the 'tick' rate of the device 'what is the length of a second' rather than just adjusting the clock time every x seconds. There are multiple variables that go into the calculations to determine how much to adjust a second. From time to time there may need to be a time step event to help the meter's clock adjust to match the NTP server's time. If this jump is greater than the threshold you will see the event in meter's event log, "time about to change" and "time change". Looking at the time stamp of these events you can calculate the approximate adjustment of the meter's clock.

 

"how long does the quartz crystal unit of the ION9000 or PM8000 can work correctly?" I am not 100% sure I understand the question. If you are asking what is the expected lifetime of the crystal, this will match or exceed the expected life time of the meter. Or if you are asking if okay to keep using the internal crystal, the answer is yes, this is okay.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Tomohiro-Okada
Lieutenant JG Tomohiro-Okada
Lieutenant JG

Posted: ‎2022-07-10 05:10 PM

0 Likes
2
1033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-10 05:10 PM

Hi @Charles_Murison,

 

Thank you for your kind reply.

 

My question about crystal was asking if okay to keep using the internal crystal and I understand what you said.

I changed the setting from "Line Freq" to "Internal" and it works well until now.

 

Regards,

Okada

Tags (1)
  • Tags:
  • english
Reply
Tomohiro-Okada
Lieutenant JG Tomohiro-Okada
Lieutenant JG

Posted: ‎2022-07-11 02:33 AM . Last Modified: ‎2022-07-11 05:05 PM

0 Likes
1
1021
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-11 02:33 AM

Hi @Charles_Murison  and @DanL,

 

Sorry to bother you again,

 but I was asked from our customer to inquire  some questions.

 

I corrected the settings of PM8000 and ION9000 from "Line Freq" to "Internal" and the other settings are below.

 

Advanced Ethernet - NTP
CL1 Enable NTP Time Sync NTP
CL1 NTP Time Sync Interval 1 day
CL1 Event Logging Threshold 0.02
ETH1 NTP Server 192.168.000.010

 

Clock - Timezone
CL1 Time Sync Type UTC
CL1 Time Sync Source ETHERNET
CL1 Clock Source Internal  (changed from "Line Freq")

 

In this case, the time synchronization works well but only the timing of the NTP synchronization is still looked random.
(time sync was done randomly per one hour or 2 hours.)

 

Does it work correctly?
(I understand NTP is more complex than SNTP and the interval is decided by many factors from your answer,
 but we needs your official answer that it is working correct.)

 

If the setting of "CL1 Enable NTP Time Sync" is "NTP" (not "SNTP"), is the setting of "CL1 NTP Time Sync Interval 1day" completely not used ? or has some meanings?(for example, roughly sync with NTP server per "1day")

 

Which do you recommend, "NTP" or "SNTP"?

 

Thanks,

Okada

 

 

 

 

 

 

 

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2022-07-11 04:25 PM

0 Likes
0
1006
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-11 04:25 PM

Hello @Tomohiro-Okada 

 

If the meter is set to use NTP, the interval is not configurable in the meter settings so 1 or 2 requests per hour is not unreasonable. One request per hour or 2 hours even is not a bad sign. The setting "CL1 NTP Time Sync Interval" is not used by the meter when setting is NTP. 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc