The timing of NTP synchronization of the ION meters.

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Re: The timing of NTP synchronization of the ION meters.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
526
Mehran_Mehrnia
Admiral Mehran_Mehrnia Admiral
138
Ramasamy_N
Captain Ramasamy_N Captain
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Tomohiro-Okada
Lieutenant Tomohiro-Okada
Lieutenant

Posted: ‎2022-06-30 01:32 AM

0 Likes
7
3808
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-30 01:32 AM

The timing of NTP synchronization of the ION meters.

Hi 

 

I have two questions about time synchronization of ION9000.

 

I did time synchronization settings of the ION9000 meter(sync with NTP server via Ethernet.)

and the time synchronization worked well.

 

The meter settings are below.

 

Metering Setup - Nameplate Info
FAC1 DeviceType 9000
FAC1 Revision 003.001.000
FAC1 Feature Set Standard

FAC1 Template 9000_V3.1.0.0.0

 

Advanced Ethernet - NTP
CL1 Enable NTP Time Sync NTP
CL1 NTP Time Sync Interval 1 day
CL1 Event Logging Threshold 0.02
ETH1 NTP Server 192.168.000.010
CL1 Time Sync Type UTC
CL1 Time Sync Source ETHERNET

 

but  only the cycle of the time sync looked random.

(In spite of the "NTP Time Sync Interval" setting was "1day",

 the Event history of the synchronization  with NTP server was  roughly about every hour.

About 20 times time synchronization was done in a day.)

 

Why was this happened?

 

The second question is the timing of the time synchronization.

 

For example, If I set the  "NTP Time Sync Interval"  setting to "1day" and the first time sync was 2022/06/30 09:00.

The next time sync will be 2022/07/01 09:00 I think.

But, the event history of the time sync was not so.

What factors decide the timing?

and can I define the timing of the synchronization?

 

Regards,

Okada

 

 

 

 

 

Labels
  • Labels:
  • ION9000
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2022-07-04 10:12 AM

0 Likes
3
3693
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-04 10:12 AM

Hello @Tomohiro-Okada ,

 

If the meter is set to SNTP, each time packet received by the meter should contain specific information, What time the meter sent the SNTP request, what time the NTP server got the request and what time NTP server sent the response. The meter would calculate the delta or transit time based on these three pieces of information as as well the local time on the meter when the packet was received by the meter. Based on this delta calculation and the SNTP/NTP servers' timestamps, the clock on the meter is adjusted.

 

NTP is significantly more complex. NTP uses complex statistical algorithms, aimed at filtering small discrepancies. NTP is intended to adjust the 'tick' rate of the device 'what is the length of a second' rather than just adjusting the clock time every x seconds. There are multiple variables that go into the calculations to determine how much to adjust a second. From time to time there may need to be a time step event to help the meter's clock adjust to match the NTP server's time. If this jump is greater than the threshold you will see the event in meter's event log, "time about to change" and "time change". Looking at the time stamp of these events you can calculate the approximate adjustment of the meter's clock.

 

"how long does the quartz crystal unit of the ION9000 or PM8000 can work correctly?" I am not 100% sure I understand the question. If you are asking what is the expected lifetime of the crystal, this will match or exceed the expected life time of the meter. Or if you are asking if okay to keep using the internal crystal, the answer is yes, this is okay.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 7
DanL
Captain DanL Captain
Captain

Posted: ‎2022-06-30 09:40 AM

1 Like
6
3783
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-06-30 09:40 AM

The unfortunately named "CL1 NTP Time Sync Interval" can only configure SNTP time sync intervals (not NTP).

Be sure to configure the "CL1 Clock Source" to "Internal" ("COMM" is also acceptable as with NTP enabled it will behave as "Internal"). Never use an external time sync source with the Clock Source configured to "Line Freq".

 

If you continue to have issues, please contact support for additional troubleshooting steps

Tags (1)
  • Tags:
  • english
Reply
Tomohiro-Okada
Lieutenant Tomohiro-Okada
Lieutenant

Posted: ‎2022-07-01 12:32 AM

0 Likes
5
3766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-01 12:32 AM

Hi @DanL 

 

Thank you for your reply.

 

So if the protocol is "NTP"(not "SNTP"), is the timing of the time sync random?

 

And if I change  the  "CL1 Clock Source" setting to "Internal", how long does the quartz crystal unit of the ION9000 or PM8000

can work correctly?

 

I'd like to know the product lifetime of the quartz crystal unit.

 

Regards,

Okada

 

 

 

Tags (1)
  • Tags:
  • english
Reply
Tomohiro-Okada
Lieutenant Tomohiro-Okada
Lieutenant

Posted: ‎2022-07-01 12:53 AM

0 Likes
4
3762
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-01 12:53 AM

Hi @DanL,

 

I have one more question.

 

If the protocol is "NTP"(not "SNTP"), does the gap of the time between PQM and NTP server affects time sync interval?

What factors decide the execution timing of the time sync when the protocol is "NTP"(not SNTP)?

 

Thanks,

Okada

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2022-07-04 10:12 AM

0 Likes
3
3694
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-04 10:12 AM

Hello @Tomohiro-Okada ,

 

If the meter is set to SNTP, each time packet received by the meter should contain specific information, What time the meter sent the SNTP request, what time the NTP server got the request and what time NTP server sent the response. The meter would calculate the delta or transit time based on these three pieces of information as as well the local time on the meter when the packet was received by the meter. Based on this delta calculation and the SNTP/NTP servers' timestamps, the clock on the meter is adjusted.

 

NTP is significantly more complex. NTP uses complex statistical algorithms, aimed at filtering small discrepancies. NTP is intended to adjust the 'tick' rate of the device 'what is the length of a second' rather than just adjusting the clock time every x seconds. There are multiple variables that go into the calculations to determine how much to adjust a second. From time to time there may need to be a time step event to help the meter's clock adjust to match the NTP server's time. If this jump is greater than the threshold you will see the event in meter's event log, "time about to change" and "time change". Looking at the time stamp of these events you can calculate the approximate adjustment of the meter's clock.

 

"how long does the quartz crystal unit of the ION9000 or PM8000 can work correctly?" I am not 100% sure I understand the question. If you are asking what is the expected lifetime of the crystal, this will match or exceed the expected life time of the meter. Or if you are asking if okay to keep using the internal crystal, the answer is yes, this is okay.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Tomohiro-Okada
Lieutenant Tomohiro-Okada
Lieutenant

Posted: ‎2022-07-10 05:10 PM

0 Likes
2
3613
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-10 05:10 PM

Hi @Charles_Murison,

 

Thank you for your kind reply.

 

My question about crystal was asking if okay to keep using the internal crystal and I understand what you said.

I changed the setting from "Line Freq" to "Internal" and it works well until now.

 

Regards,

Okada

Tags (1)
  • Tags:
  • english
Reply
Tomohiro-Okada
Lieutenant Tomohiro-Okada
Lieutenant

Posted: ‎2022-07-11 02:33 AM . Last Modified: ‎2022-07-11 05:05 PM

0 Likes
1
3601
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-11 02:33 AM

Hi @Charles_Murison  and @DanL,

 

Sorry to bother you again,

 but I was asked from our customer to inquire  some questions.

 

I corrected the settings of PM8000 and ION9000 from "Line Freq" to "Internal" and the other settings are below.

 

Advanced Ethernet - NTP
CL1 Enable NTP Time Sync NTP
CL1 NTP Time Sync Interval 1 day
CL1 Event Logging Threshold 0.02
ETH1 NTP Server 192.168.000.010

 

Clock - Timezone
CL1 Time Sync Type UTC
CL1 Time Sync Source ETHERNET
CL1 Clock Source Internal  (changed from "Line Freq")

 

In this case, the time synchronization works well but only the timing of the NTP synchronization is still looked random.
(time sync was done randomly per one hour or 2 hours.)

 

Does it work correctly?
(I understand NTP is more complex than SNTP and the interval is decided by many factors from your answer,
 but we needs your official answer that it is working correct.)

 

If the setting of "CL1 Enable NTP Time Sync" is "NTP" (not "SNTP"), is the setting of "CL1 NTP Time Sync Interval 1day" completely not used ? or has some meanings?(for example, roughly sync with NTP server per "1day")

 

Which do you recommend, "NTP" or "SNTP"?

 

Thanks,

Okada

 

 

 

 

 

 

 

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2022-07-11 04:25 PM

0 Likes
0
3586
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-11 04:25 PM

Hello @Tomohiro-Okada 

 

If the meter is set to use NTP, the interval is not configurable in the meter settings so 1 or 2 requests per hour is not unreasonable. One request per hour or 2 hours even is not a bad sign. The setting "CL1 NTP Time Sync Interval" is not used by the meter when setting is NTP. 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.