Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Replace old ION meters

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Replace old ION meters
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Stuart_Cheng
Stuart_Cheng Contributor
Contributor

Posted: ‎2022-08-05 02:16 AM

0 Likes
5
2830
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-05 02:16 AM

Replace old ION meters

Hi All,

 

At one customer site, we are going to replace several old PM8000 meters. I plan the following procedure, would like to check if anything wrong.

 

1. Upgrade the firmware of the old PM8000 (to the version of the new PM8000)
2. Export the .dcf file from the old PM8000
3. Import the .dcf file into new PM8000

 

Based on the procedure abovementioned, am I be able to copy the configuration and framework to the new meters without any further settings? Do I also need to copy the .cfg file to see the layout of the framework?

 

Thank you.

Best regards,

 

Labels
  • Labels:
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2022-08-05 09:51 AM

2 Likes
4
2816
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-05 09:51 AM

Hello @Stuart_Cheng ,

 

If you are going to be replacing the meters, upgrading the firmware first is likely just a waste of time. I would recommend determining if the existing template has any customizations (manual process), record information like, customizations, PT/CT ratios, nominal voltage, volts mode, energy readings, alarm settings sag/swell settings etc. Then use a new meter with new template and apply the settings of the original meter plus any customizations.

 

When upgrading firmware on an ION Meter, onboard memory including the template are erased. Be sure that any logged data you want to keep is saved before upgrading. When upgrading, most configuration information has the option to be saved to temp location and put back on the meter after upgrade.

 

Most elements of a meter's template are future compactable, that is to say, new firmware can support older templates. The better question to ask is should older templates be put on newer firmware. Often firmware updates will allow for new features or updates that did not exist on the older firmware. If the old template is used, some of these features may not be used or used to full potential. An example of this is with old firmware, 2 PQ standards could not be implemented on the same meter, there was 1 template for IEE519 and a standard template. Now the meter supports enough modules to have both. 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 5
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2022-08-05 09:51 AM

2 Likes
4
2816
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-05 09:51 AM

Hello @Stuart_Cheng ,

 

If you are going to be replacing the meters, upgrading the firmware first is likely just a waste of time. I would recommend determining if the existing template has any customizations (manual process), record information like, customizations, PT/CT ratios, nominal voltage, volts mode, energy readings, alarm settings sag/swell settings etc. Then use a new meter with new template and apply the settings of the original meter plus any customizations.

 

When upgrading firmware on an ION Meter, onboard memory including the template are erased. Be sure that any logged data you want to keep is saved before upgrading. When upgrading, most configuration information has the option to be saved to temp location and put back on the meter after upgrade.

 

Most elements of a meter's template are future compactable, that is to say, new firmware can support older templates. The better question to ask is should older templates be put on newer firmware. Often firmware updates will allow for new features or updates that did not exist on the older firmware. If the old template is used, some of these features may not be used or used to full potential. An example of this is with old firmware, 2 PQ standards could not be implemented on the same meter, there was 1 template for IEE519 and a standard template. Now the meter supports enough modules to have both. 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Tom_Stevenson
Tom_Stevenson Champion
Champion

Posted: ‎2022-08-05 10:03 AM

0 Likes
0
2814
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-05 10:03 AM

Fully agreed with Charles - if you have customizations to ION frameworks from the factory default, I would suggest you maintain a sub-framework you can apply to the latest factory framework.  This way, you can take the latest factory framework and paste your set of modifications in Designer to it to produce your custom default framework.  This is a very context specific question too, so please advise if there are other nuances to consider.


Tom

Tags (1)
  • Tags:
  • english
Reply
Stuart_Cheng
Stuart_Cheng Contributor
Contributor

Posted: ‎2022-08-07 06:46 PM

0 Likes
2
2756
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-07 06:46 PM

Hi Both,

 

Many thanks for your information and I can see that upgrading the old ION meters is not necessary since the templates are future compatible.

 

Would like to check again if I understand correctly. The recommended way from your side is to identify the customization of the old ION meter and paste them onto the new ION meter via Designer. The reason is that importing the .dcf file from the old ION meter may not fully bring out the potential of the new firmware?

 

Thank you.

Best regards,

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2022-08-08 09:55 AM

1 Like
1
2734
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-08 09:55 AM

Hello @Stuart_Cheng 

 

"Would like to check again if I understand correctly. The recommended way from your side is to identify the customization of the old ION meter and paste them onto the new ION meter via Designer. The reason is that importing the .dcf file from the old ION meter may not fully bring out the potential of the new firmware?"

Correct

 

"Many thanks for your information and I can see that upgrading the old ION meters is not necessary since the templates are future compatible."

As stated may be a little confusing. Every effort is taken to make new versions of firmware compatible with older templates. Current firmware can have older templates placed on. There may be some change in a future firmware where an existing template would no longer be able to be placed on new firmware. For example if modules are deprecated. (see Pinned post as of typing this replay). Most modules currently listed for deprecation are not used in default framework.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Stuart_Cheng
Stuart_Cheng Contributor
Contributor

Posted: ‎2022-08-08 06:14 PM

0 Likes
0
2721
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-08 06:14 PM

Hi @Charles_Murison 

 

It’s clear. Thanks for the help!

 

Best regards,

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore