why VPL6 reads 0.7 capacitive power factor

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • why VPL6 reads 0.7 capacitive power factor
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
MohanadRamadan
MohanadRamadan
Cadet

Posted: ‎2022-07-23 04:49 AM

1 Like
1
971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-07-23 04:49 AM

why VPL6 reads 0.7 capacitive power factor

when commissioning the varplus logic regulator after configuring CT parameter and initiating AI the controller reads 0.7c and none of the steps is active. the question here why does the controller read lead power factor ? although the Delta Q equals 990 var and the smallest step is 5kVAR

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Arunprasad
Lt. Commander Arunprasad Lt. Commander
Lt. Commander

Posted: ‎2022-08-09 08:48 AM

1 Like
0
897
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-09 08:48 AM

Hello  MohanadRamadan ,

I apologize for the delay in our response.

Here below are our thoughts.
The PFC Controller can read 0.7c, because the load is really capacitive.
Since the loads are less, then  it is not rare to see cos pi  as capacitive.
DQ is very low,  it can be the real condition, or the CT ration can be wrong. Else you might not set the Angle correctly.
But here the  Ai was done,so we can expect angle is set correctly,in this case you should try to put some reactive load and see how the controller react,
I mean,does current increase proportionally to load the you just connect , does the cos  phi move  to an inductive value .  
Do you have a meter somewhere to compare the controller  current and cos phi with another meter.

Another option, you can also just force a step in fix On ( in the Out parameter in menu 100)  and see if the controller read a correct value .
If angle is totally wrong or CT not set correctly then you will be able to notice it.

You can also compares P & Q  value before and after, where the P should be nearly  the same and the Q should be the initial value.


For Example (1KVAR C + the step value and if the step is 5KVAR C)you should obtain 6KVAR C.
So if the values are not as expected, then it is an issue with the CT ratio or the cabling is not correct.

 

If you still had an issue, please connect with the country CCC team and raise a BFO Case and share your findings, like images and videos captured.

 

 

 

 

Arunprasad

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Reply 1
Arunprasad
Lt. Commander Arunprasad Lt. Commander
Lt. Commander

Posted: ‎2022-08-09 08:48 AM

1 Like
0
898
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-09 08:48 AM

Hello  MohanadRamadan ,

I apologize for the delay in our response.

Here below are our thoughts.
The PFC Controller can read 0.7c, because the load is really capacitive.
Since the loads are less, then  it is not rare to see cos pi  as capacitive.
DQ is very low,  it can be the real condition, or the CT ration can be wrong. Else you might not set the Angle correctly.
But here the  Ai was done,so we can expect angle is set correctly,in this case you should try to put some reactive load and see how the controller react,
I mean,does current increase proportionally to load the you just connect , does the cos  phi move  to an inductive value .  
Do you have a meter somewhere to compare the controller  current and cos phi with another meter.

Another option, you can also just force a step in fix On ( in the Out parameter in menu 100)  and see if the controller read a correct value .
If angle is totally wrong or CT not set correctly then you will be able to notice it.

You can also compares P & Q  value before and after, where the P should be nearly  the same and the Q should be the initial value.


For Example (1KVAR C + the step value and if the step is 5KVAR C)you should obtain 6KVAR C.
So if the values are not as expected, then it is an issue with the CT ratio or the cabling is not correct.

 

If you still had an issue, please connect with the country CCC team and raise a BFO Case and share your findings, like images and videos captured.

 

 

 

 

Arunprasad
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of