Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION9000 FCAS window monitoring

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION9000 FCAS window monitoring
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Related Products
product field
Schneider Electric
PowerLogic ION9000

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
alannavial
alannavial Explorer
Explorer

Posted: ‎2022-08-04 10:56 PM

0 Likes
2
2426
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-04 10:56 PM

ION9000 FCAS window monitoring

One of the strictest FCAS requirements we need to meet as per the attached is that when there is a frequency deviation outside of a certain range (for example of the grid frequency drops below 48.8hz) then we need to capture 60s of data after the trigger point but also 5s before (in 20ms granularity).

alannavial_0-1659678772070.png

 

 

Referring to the manual attached for the ION9000 on page 217 there is information on ‘Extended Waveform Capture’

alannavial_1-1659678772164.png

 

 

How long can the C and D periods in the above diagram be and how easy can the values be changed? We need the pre event period to be 5s and the post event recording to be 60s.

 

Can the ION9000 easily be configured to capture such events?  If so, how would I do this?

 

  • Thumbnail of PowerLogic ION9000
    Schneider Electric
    PowerLogic ION9000
View products (1)
Labels
  • Labels:
  • ION9000
Tags (2)
  • Tags:
  • english
  • FCAS
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DanL
DanL Champion
Champion

Posted: ‎2022-08-05 09:15 AM

3 Likes
1
2405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-05 09:15 AM

That one bullet point looks like it is from Australian FCAS requirements?

If so the context matters, because that requirement is not for instantaneous voltage (ie. waveform capture), but instead for co-incident "high-speed" frequency and power measurements.
I would recommend using a setpoint module to trigger a DataRecorder configured with pre-trigger and post-trigger records.
https://www.productinfo.schneider-electric.com/ion9000/viewer?docidentity=DataRecorderModule-21B4C52...

With the DataRecorder's inputs linked to The HighSpeed PowerMeter module's "HS Freq" and "HS kW tot" outputs, it will collect data every half-cycle.
For example:
Pre-Trigger records = 500 (5s)

Post-Trigger records = 6000 (60s)

Buffer Depth = 13002 (two full captures fully buffered)

Depth = 65010 (internal storage for 10 full captures)

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 2
DanL
DanL Champion
Champion

Posted: ‎2022-08-05 09:15 AM

3 Likes
1
2405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-05 09:15 AM

That one bullet point looks like it is from Australian FCAS requirements?

If so the context matters, because that requirement is not for instantaneous voltage (ie. waveform capture), but instead for co-incident "high-speed" frequency and power measurements.
I would recommend using a setpoint module to trigger a DataRecorder configured with pre-trigger and post-trigger records.
https://www.productinfo.schneider-electric.com/ion9000/viewer?docidentity=DataRecorderModule-21B4C52...

With the DataRecorder's inputs linked to The HighSpeed PowerMeter module's "HS Freq" and "HS kW tot" outputs, it will collect data every half-cycle.
For example:
Pre-Trigger records = 500 (5s)

Post-Trigger records = 6000 (60s)

Buffer Depth = 13002 (two full captures fully buffered)

Depth = 65010 (internal storage for 10 full captures)

Tags (1)
  • Tags:
  • english
Reply
alannavial
alannavial Explorer
Explorer

Posted: ‎2022-08-10 06:47 PM

1 Like
0
2316
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-10 06:47 PM

Hi Dan,

Thank you for the help.  You answered my question perfectly!

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore