hi all,
Where can i find the on/off voltage range of the digital input signal on the ION7650?
Can you tell me the information about the range of on/off state for ion7650 as above?
thanks a lot.
Best regarlds
Link copied. Please paste this link to share this article on your social media post.
The ION7650 digital inputs have internal "self-excitation" and will register as "Closed" when an Sn (n=1 to 8 ) digital input is connected to Scom with a voltage between 0V (short) and 130VDC.
Link copied. Please paste this link to share this article on your social media post.
Hello @mimi1002,
The screenshot you provided is likely from ION9000, PM800 or ION7400 meter. The ION7650 meters uses a completely different design. There are no ranges, there is open or there is close.
https://www.se.com/ww/en/download/document/70002-0247/, page 11. The digital inputs require Open/Close signal with or without external DC voltage.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
The ION7650 digital inputs have internal "self-excitation" and will register as "Closed" when an Sn (n=1 to 8 ) digital input is connected to Scom with a voltage between 0V (short) and 130VDC.