Where can i find the on/off voltage range of the digital input signal on the ION7650?

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Where can i find the on/off voltage range of the digital input signal on the ION7650?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All
Related Products
product field
Schneider Electric
EcoStruxure™ Power Advisor

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
mimi1002
Ensign mimi1002
Ensign

Posted: ‎2022-08-07 10:01 PM . Last Modified: ‎2022-08-07 10:03 PM

0 Likes
2
1124
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-07 10:01 PM

Where can i find the on/off voltage range of the digital input signal on the ION7650?

hi all,

 

Where can i find the on/off voltage range of the digital input signal on the ION7650?

 

asd.png

 

Can you tell me the information about the range of on/off state for ion7650 as above?

 

thanks a lot.

 

Best regarlds

  • Thumbnail of EcoStruxure™ Power Advisor
    Schneider Electric
    EcoStruxure™ Power Advisor
View products (1)
Labels
  • Labels:
  • ION7000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DanL
Captain DanL Captain
Captain

Posted: ‎2022-08-08 10:39 AM . Last Modified: ‎2022-08-18 03:22 PM

1 Like
0
1097
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-08 10:39 AM

The ION7650 digital inputs have internal "self-excitation" and will register as "Closed" when an Sn (n=1 to 8 ) digital input is connected to Scom with a voltage between 0V (short) and 130VDC.

  • A wire with less than 10k Ohms (ideally less than 1 Ohm) across the terminals will register as CLOSED.
  • A connection with a (non-negative) voltage up to 130VDC applied (ideally less than 30VDC) will register as CLOSED.
  • A negative voltage exceeding -20V is applied (recommended practice is to provide an open circuit instead of a negative voltage) will register as OPEN.
  • A connection with more than 1Meg Ohms (ideally more than 10 Meg Ohm) across the terminals will register as OPEN.

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 2
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2022-08-08 09:19 AM

0 Likes
1
1103
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-08 09:19 AM

Hello @mimi1002,

 

The screenshot you provided is likely from ION9000, PM800 or ION7400 meter. The ION7650 meters uses a completely different design. There are no ranges, there is open or there is close.

https://www.se.com/ww/en/download/document/70002-0247/, page 11. The digital inputs require Open/Close signal with or without external DC voltage.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
DanL
Captain DanL Captain
Captain

Posted: ‎2022-08-08 10:39 AM . Last Modified: ‎2022-08-18 03:22 PM

1 Like
0
1098
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-08 10:39 AM

The ION7650 digital inputs have internal "self-excitation" and will register as "Closed" when an Sn (n=1 to 8 ) digital input is connected to Scom with a voltage between 0V (short) and 130VDC.

  • A wire with less than 10k Ohms (ideally less than 1 Ohm) across the terminals will register as CLOSED.
  • A connection with a (non-negative) voltage up to 130VDC applied (ideally less than 30VDC) will register as CLOSED.
  • A negative voltage exceeding -20V is applied (recommended practice is to provide an open circuit instead of a negative voltage) will register as OPEN.
  • A connection with more than 1Meg Ohms (ideally more than 10 Meg Ohm) across the terminals will register as OPEN.
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of