Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PowerLogic PM5563 Data Log Loss of Precision after 1B Wh

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PowerLogic PM5563 Data Log Loss of Precision after 1B Wh
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
566
Mehran_Mehrnia
Mehran_Mehrnia Champion
194
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Related Products
product field
Schneider Electric
PowerLogic PM5000 series

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
NortheastSolar
NortheastSolar
Explorer

Posted: ‎2024-07-14 08:15 PM

0 Likes
4
2142
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-14 08:15 PM

PowerLogic PM5563 Data Log Loss of Precision after 1B Wh

We have come across an unfortunate behavior in the Ion Setup Data Log retrieval for PM5563 meters

 

Up until one shy of a billion on the meter, retrieving the Wh Data Log would produce a listing of 15-minute intervals precise to 1 watt-hours

 

As soon as the meter went over 1B, the log retrieval started using scientific notation precise only to the one-million-th watt hours. If I log into the meter's web interface directly, the wh counter is correct.

 

So for example on the meter web interface:

1006467208 Wh

is only being transmitted to Ion Setup as:

1006000000 Wh

 

How can Ion Setup be configured to retrieve data accurate to 1 Wh again?

 

Thanks in advance

 

  • Thumbnail of PowerLogic PM5000 series
    Schneider Electric
    PowerLogic PM5000 series
View products (1)
Labels
  • Labels:
  • ION Setup
  • PM5000
Tags (5)
  • Tags:
  • Data Log
  • english
  • ion setup
  • Loss of Precision
  • pm5563
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2024-07-16 09:42 AM . Last Modified: ‎2024-07-16 09:43 AM

1 Like
0
2085
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-16 09:42 AM

What version of ION Setup are you using?  I suggest downloading the latest version from the following location: ION Setup Latest Release | Schneider Electric

Depending on how long ago the device has been since the data log has been programmed, you may need to reprogram the data log again with the latest version which should permit the UINT64 version of the energy registers and not the FLOAT32 version (which is what I believe is happening).

Below I've reprogrammed my PM556X device data log with the latest version and preset the energy register to the same number as you posted above and it is showing up fine.

Robert_Lee_0-1721147978726.png

 




See Answer In Context

Reply
Replies 4
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2024-07-15 02:54 PM

0 Likes
1
2118
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-15 02:54 PM

Hello @NortheastSolar ,

 

There are a number of factors that can come into play here. One of the big ones is what format for the number is being used. 32-bit float (IEEE 754, also know as Single-precision floating-point format) has limitations on resolution depending how big the number is. 1006467208 cannot be represented as a floating point number, the closes number would be 1006467200. The meter's web page might be using internal features such as int32, 64 bit float or some other method that cannot be used external to the meter.

When numbers get large, there is no way to keep resolution down to 1 kwh and still have large numbers when numbers are encoded with 32-bit floating point.

So short answer is no, not possible to for ION Setup. Why the resolution is that much lower in ION Setup I am not sure.

 

Regards,

Charles 

L4 Prime for Advanced metering and Utilities
Reply
NortheastSolar
NortheastSolar
Explorer

Posted: ‎2024-07-15 11:12 PM

0 Likes
0
2078
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-15 11:12 PM

Hi Charles, 10 or 100 Wh precision would be workable but as it stands one million Wh precision is essentially unusable for us.

 

So the question becomes if either of the following options are possible:

- Subtract 1B from the total before transmitting to ION, or

- Transmit 10 or 100 Wh precise numbers to ION

 

Alternatively is there an alternative to ION to retrieve 15-minute interval data?

Reply
Robert_Lee
Robert_Lee Champion
Champion

Posted: ‎2024-07-16 09:42 AM . Last Modified: ‎2024-07-16 09:43 AM

1 Like
0
2086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-07-16 09:42 AM

What version of ION Setup are you using?  I suggest downloading the latest version from the following location: ION Setup Latest Release | Schneider Electric

Depending on how long ago the device has been since the data log has been programmed, you may need to reprogram the data log again with the latest version which should permit the UINT64 version of the energy registers and not the FLOAT32 version (which is what I believe is happening).

Below I've reprogrammed my PM556X device data log with the latest version and preset the energy register to the same number as you posted above and it is showing up fine.

Robert_Lee_0-1721147978726.png

 




Reply
Kelster
Kelster
Explorer

Posted: ‎2025-06-09 08:09 AM

0 Likes
0
1216
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-06-09 08:09 AM

If I do the software update, does it delete my existing data logs?

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore