Hi team,
Have a nice day.
The PCS+ unit we installed for customer got an Over Temperture Alarm that made the unit stop. It showed "Inductor Over Temperature" in Event detail. We have search this issue in document but we couldn't find more information. Please give me some directions if anything needs taking.
Thank you in advance,
Nguyen
Link copied. Please paste this link to share this article on your social media post.
Hello Nguyen,
You mean to mention Inductor OT alarm observed during installation time itself or after period of the installation?
How about the room environment where AccuSine PCS is installed and heat sink condition from inside the AHF.
Please refer inductor OT explanation as per below,
Inductor Temperature:
We have Thermal sensor inside the Inductor, on the failure, of this Thermal sensor, we will get this issue,
This temperature will not be displayed in the HMI, but, same will be continuously monitored by the Control board.
Here below are some of the possible reasons for this issue to pop-up.
If there was intermediate contact in the connectors.
If there was any damage or defect in the wire harness, which sense the Inductor temperature.
Unfortunately, the sensor inside the Inductor becomes defective then we need to replace the entire Inductor.
This is the first connectors that connects the Inductor thermal sensor and the wire harness.
This is the 2nd connector where the sense cable are connected with the Control board.
In general, we use to get Intermediate problem in the above connector.
As shown in the above image, please do the resistance measurement between the cables, the values should be as mentioned above.
Red and Black cables are used for Inductor temperature sensor measurements .
If you find any abnormalities, that is ,if the resistance values are measured in Mega ohms, then it is a problem.
We don’t have an option, 100% we need to replace the Inductor.
But if the measurement is well within the limit, then it can be due to intermittent contact between the cables in male and female connectors.
We call this as wire pull back issue, it is very rare, but, only that should cause this issue to happen.
I hope this can resolve your Inductor temperature issue.
Thank you,
Best regards,
Swapnil
Link copied. Please paste this link to share this article on your social media post.
Thanks for reaching out. Over Temperature Alarm and eventual trip is a safety mechanism that protects the unit from further damage. I let @Swapnil get back to you with further details.
Link copied. Please paste this link to share this article on your social media post.
Hello Nguyen,
You mean to mention Inductor OT alarm observed during installation time itself or after period of the installation?
How about the room environment where AccuSine PCS is installed and heat sink condition from inside the AHF.
Please refer inductor OT explanation as per below,
Inductor Temperature:
We have Thermal sensor inside the Inductor, on the failure, of this Thermal sensor, we will get this issue,
This temperature will not be displayed in the HMI, but, same will be continuously monitored by the Control board.
Here below are some of the possible reasons for this issue to pop-up.
If there was intermediate contact in the connectors.
If there was any damage or defect in the wire harness, which sense the Inductor temperature.
Unfortunately, the sensor inside the Inductor becomes defective then we need to replace the entire Inductor.
This is the first connectors that connects the Inductor thermal sensor and the wire harness.
This is the 2nd connector where the sense cable are connected with the Control board.
In general, we use to get Intermediate problem in the above connector.
As shown in the above image, please do the resistance measurement between the cables, the values should be as mentioned above.
Red and Black cables are used for Inductor temperature sensor measurements .
If you find any abnormalities, that is ,if the resistance values are measured in Mega ohms, then it is a problem.
We don’t have an option, 100% we need to replace the Inductor.
But if the measurement is well within the limit, then it can be due to intermittent contact between the cables in male and female connectors.
We call this as wire pull back issue, it is very rare, but, only that should cause this issue to happen.
I hope this can resolve your Inductor temperature issue.
Thank you,
Best regards,
Swapnil
Link copied. Please paste this link to share this article on your social media post.
Hello Mr. @Swapnil and Mr. @Sreemant_Roy ,
Thank you for your response.
It is really helpful and intuitive. I will check according to your instructions.
Thank you for your support,
Have a nice day,
Nguyen
Link copied. Please paste this link to share this article on your social media post.
Hello @Swapnil
Thanks for your quick support and insights.
@NguyenMon Thanks for reaching us an we are happy to support you as always. But i have a request, for these kind of support, could you please approach us through BFO for better traceability. This will be very helpful in future. Also when you raise a BFO case please share the commercial reference and the respective serial number for better understanding.
Thanks for understanding.
Link copied. Please paste this link to share this article on your social media post.
Dear Mr. @Arunprasad,
Thank you for your response and support.
I understand and fully agree with your suggestion. From now on, I will submit support requests through the BFO system to ensure better tracking and more efficient handling. When creating a case, I will also include the commercial reference and the respective serial number as you advised.
Thank you once again for your support.
Best regards,
NguyenMon