AccuSine PCS+ : Over Temperature Error

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • AccuSine PCS+ : Over Temperature Error
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
NguyenMon
Lieutenant | EcoXpert Master NguyenMon Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2025-05-15 02:24 AM

1 Like
4
131
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-15 02:24 AM

AccuSine PCS+ : Over Temperature Error

Hi team,

Have a nice day.

 

The PCS+ unit we installed for customer got an Over Temperture Alarm that made the unit stop. It showed "Inductor Over Temperature" in Event detail. We have search this issue in document but we couldn't find more information. Please give me some directions if anything needs taking.

 

Thank you in advance,

Nguyen

Labels
  • Labels:
  • Power Quality
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Swapnil
Ensign Swapnil Ensign
Ensign

Posted: ‎2025-05-17 05:04 AM

3 Likes
1
72
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-17 05:04 AM

Hello Nguyen,

You mean to mention Inductor OT alarm observed during installation time itself or after period of the installation?

How about the room environment where AccuSine PCS is installed and heat sink condition from inside the AHF.

 

Please refer inductor OT explanation as per below,

Inductor Temperature:

We have Thermal sensor inside the Inductor, on the failure, of this Thermal sensor, we will get this issue,

This temperature will not be displayed in the HMI, but, same will be continuously monitored by the Control board.

Here below are some of the possible reasons for this issue to pop-up.

 

If there was intermediate contact in the connectors.

If there was any damage or defect in the wire harness, which sense the Inductor temperature.

Unfortunately, the sensor inside the Inductor becomes defective then we need to replace the entire Inductor.

This is the first connectors that connects the Inductor thermal sensor and the wire harness.

Swapnil_0-1747483174891.png

 

 

This is the 2nd connector where the sense cable are connected with the Control board.

Swapnil_1-1747483174909.png

 

In general, we use to get Intermediate problem in the above connector.

 

Swapnil_2-1747483174947.png

 

 

Swapnil_3-1747483174978.png

 

 

As shown in the above image, please do the resistance measurement between the cables, the values should be as mentioned above.

Red and Black cables are used for Inductor temperature sensor measurements .

If you find any abnormalities, that is ,if the resistance values are measured in Mega ohms, then it is a problem.

We don’t have an option, 100% we need to replace the Inductor.

But if the measurement is well within the limit, then it can be due to intermittent contact between the cables in male and female connectors. 

Swapnil_4-1747483175005.png

 

We call this as wire pull back issue, it is very rare, but, only that should cause this issue to happen.

I hope this can resolve your Inductor temperature issue.

 

Thank you,

Best regards,

Swapnil

See Answer In Context

Reply
Replies 4
Sreemant_Roy
Ensign Sreemant_Roy Ensign
Ensign

Posted: ‎2025-05-16 05:38 AM

2 Likes
2
98
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-16 05:38 AM

Thanks for reaching out. Over Temperature Alarm and eventual trip is a safety mechanism that protects the unit from further damage. I let @Swapnil get back to you with further details. 

Sreemant Roy
Product Owner - Active Power Quality Solutions ( AccuSine & DVR's )
Reply
Swapnil
Ensign Swapnil Ensign
Ensign

Posted: ‎2025-05-17 05:04 AM

3 Likes
1
73
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-17 05:04 AM

Hello Nguyen,

You mean to mention Inductor OT alarm observed during installation time itself or after period of the installation?

How about the room environment where AccuSine PCS is installed and heat sink condition from inside the AHF.

 

Please refer inductor OT explanation as per below,

Inductor Temperature:

We have Thermal sensor inside the Inductor, on the failure, of this Thermal sensor, we will get this issue,

This temperature will not be displayed in the HMI, but, same will be continuously monitored by the Control board.

Here below are some of the possible reasons for this issue to pop-up.

 

If there was intermediate contact in the connectors.

If there was any damage or defect in the wire harness, which sense the Inductor temperature.

Unfortunately, the sensor inside the Inductor becomes defective then we need to replace the entire Inductor.

This is the first connectors that connects the Inductor thermal sensor and the wire harness.

Swapnil_0-1747483174891.png

 

 

This is the 2nd connector where the sense cable are connected with the Control board.

Swapnil_1-1747483174909.png

 

In general, we use to get Intermediate problem in the above connector.

 

Swapnil_2-1747483174947.png

 

 

Swapnil_3-1747483174978.png

 

 

As shown in the above image, please do the resistance measurement between the cables, the values should be as mentioned above.

Red and Black cables are used for Inductor temperature sensor measurements .

If you find any abnormalities, that is ,if the resistance values are measured in Mega ohms, then it is a problem.

We don’t have an option, 100% we need to replace the Inductor.

But if the measurement is well within the limit, then it can be due to intermittent contact between the cables in male and female connectors. 

Swapnil_4-1747483175005.png

 

We call this as wire pull back issue, it is very rare, but, only that should cause this issue to happen.

I hope this can resolve your Inductor temperature issue.

 

Thank you,

Best regards,

Swapnil

Reply
NguyenMon
Lieutenant | EcoXpert Master NguyenMon Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2025-05-18 08:48 AM

2 Likes
0
41
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-18 08:48 AM

Hello Mr. @Swapnil and Mr. @Sreemant_Roy ,

 

Thank you for your response.

It is really helpful and intuitive. I will check according to your instructions.

 

Thank you for your support,

Have a nice day,

Nguyen

 

Reply
Arunprasad
Lt. Commander Arunprasad Lt. Commander
Lt. Commander

Posted: ‎2025-05-19 02:46 AM

1 Like
0
24
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-19 02:46 AM

Hello @Swapnil 

Thanks for your quick support and insights.

@NguyenMon  Thanks for reaching us an we are happy to support you as always. But i have a request, for these kind of support, could you please approach us through BFO for better traceability. This will be very helpful in future. Also when you raise a BFO case please share the commercial reference and the respective serial number for better understanding.

Thanks for understanding.

Arunprasad
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of