PM8000 – Modbus TCP/IP Node ID

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000 – Modbus TCP/IP Node ID
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
498
Ramasamy_N
Captain Ramasamy_N Captain
115
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
98
Robert_Lee
Admiral Robert_Lee Admiral
92
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Gilbert
Gilbert
Cadet

Posted: ‎2025-06-04 10:48 AM

0 Likes
2
208
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-06-04 10:48 AM

PM8000 – Modbus TCP/IP Node ID

PM8000 – Modbus TCP/IP Node ID

With respect to the PM8244, the clients BMS software (Tridium, Niagara Framework) will not allow a node ID of 0 or 255.

Issue:

Upgrading from PM800 to PM8000 meters (39 meters), each meter has many Modbus RTU slaves (Meter as a Gateway). PM800 allowed to set the Node address to 1-248 for the TCP connection.

If we turn off the gateway function of the meter, the BMS will communicate and read meter data, as soon as we turn on the gateway (Modbus Master, Com1, Node ID 1) all RTU nodes communicate, but the PM8000 data stops.

Question:

Is there a was to set the TCP/IP Node ID between 1-248?

With Firmware V4.6, I see that BACnet can be used. Can the BMS talk to the PM8000 on BacNet and the meter still use the Gateway function (Modbus Master)?

Labels
  • Labels:
  • ION Setup
  • PM8000
  • Power Quality
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-06-05 09:18 AM

0 Likes
0
193
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-06-05 09:18 AM

Hello @Gilbert,
"Is there a was to set the TCP/IP Node ID between 1-248?"

-No, sadly, when gateway function is active, meter will only respond to ID 255.

"With Firmware V4.6, I see that BACnet can be used. Can the BMS talk to the PM8000 on BacNet and the meter still use the Gateway function (Modbus Master)?"

Yes, meter can have multiple protocols talk to the meter at the same time.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 2
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-06-05 09:18 AM

0 Likes
0
194
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-06-05 09:18 AM

Hello @Gilbert,
"Is there a was to set the TCP/IP Node ID between 1-248?"

-No, sadly, when gateway function is active, meter will only respond to ID 255.

"With Firmware V4.6, I see that BACnet can be used. Can the BMS talk to the PM8000 on BacNet and the meter still use the Gateway function (Modbus Master)?"

Yes, meter can have multiple protocols talk to the meter at the same time.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Gilbert
Gilbert
Cadet

Posted: ‎2025-06-05 01:10 PM

0 Likes
0
140
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-06-05 01:10 PM

Charles, Thank you for the timely response.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of