I'm curious if a 3rd CT can be connected to I4 on the PM8000 to directly measure the Neutral current, and therefore calculate ground leakage current in a 1PH3W LL with N configuration. I see this is an option for 3-phase, but not explicitly shown for a single-phase system. I've attached a sketch. I have an open case with support, but was wondering if anyone here has experience with this setup. Thanks!
- Labels:
-
PM8000
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @BrandonReed ,
I have not tried this myself personally, talking with one of the developers, this configuration was his recommendation.
Regards,
Charles
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @BrandonReed ,
I have not tried this myself personally, talking with one of the developers, this configuration was his recommendation.
Regards,
Charles
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Thanks, @Charles_Murison. Is it your understanding that the meter is capable of reading all three CTs and performing the calculation in this configuration? I was trying to get confirmation prior to purchasing three CTs instead of two. Thanks again!
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @BrandonReed , that is my understanding.
Regards,
Charles