Hello,
Is it possible to read Digital Input Status using Ethernet/IP? I see that we are able from Modbus Register 8905 and also in BACnet.
Link copied. Please paste this link to share this article on your social media post.
Hello @emendoz7 @Jesus_Diaz
Yes, currently the Digital input and output status objects are not enabled in the Ethernet/IP protocol.
I will add this request to check the feasibility check in future.
Regards,
Ramasamy N
Link copied. Please paste this link to share this article on your social media post.
Hello,
There is no option for reading digital input status for the EtherNet/IP protocol in the user guide or CID file.
@Ramasamy_N Could you please confirm?
Link copied. Please paste this link to share this article on your social media post.
Hello @emendoz7 @Jesus_Diaz
Yes, currently the Digital input and output status objects are not enabled in the Ethernet/IP protocol.
I will add this request to check the feasibility check in future.
Regards,
Ramasamy N