How to find out Modbus Register address or Output Register for TDD on PM8240 and ION7400
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
When looking at the ION7400 V4.5.0 Modbus mapping excel file I see the same TDD registers as PM8000 meter. One item to note is that this TDD is from the IEE519 framework. You will need to configure IEEE519 or at least the External numeric 519_I_L in meter for the TDD calculations. The modules performing the TDD are Harmonic Measurement Modules.
When looking at the ION7400 V4.5.0 Modbus mapping excel file I see the same TDD registers as PM8000 meter. One item to note is that this TDD is from the IEE519 framework. You will need to configure IEEE519 or at least the External numeric 519_I_L in meter for the TDD calculations. The modules performing the TDD are Harmonic Measurement Modules.