Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

PM5340 meter Mac Address for DHCP does not match Mac Address on meter label or display

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM5340 meter Mac Address for DHCP does not match Mac Address on meter label or display
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
sesa37232_bridg
sesa37232_bridg Explorer
Explorer

Posted: ‎2024-02-20 03:37 PM

0 Likes
1
1186
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-02-20 03:37 PM

PM5340 meter Mac Address for DHCP does not match Mac Address on meter label or display

A customer is using the Mac Addresses to reserve IP addresses for some PM5340 meters on their system. The DHCP server has been configured to reserve IP addresses base on the Meter Mac Address. When the DHCP server request the Mac address from the meter the response from the meter does not match the Mac Address on the meter. 
As an example meter responds with a Mac address of 504d353334305f30303336383439. Based on the meter's display and label the meter's Mac Address is 00:80:67:8E:07:0C. The meter's Serial Number is 540120036849. The OS is 2.15, The RS is 2.0.0 and the Language is 4.2.0.
Why does the meter respond with a strange Mac Address when it is requested by the DHCP server? Is there a setting that is required on the meter for it to respond with a Mac address that matches the meter display and label?

Labels
  • Labels:
  • PM5000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2024-03-04 08:45 AM . Last Modified: ‎2024-03-04 08:46 AM

1 Like
0
1137
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-03-04 08:45 AM

Hello @sesa37232_bridg 

The device identifier response from PM5340 for DHCP server 504d353334305f30303336383439 is device name like PM5340_followed by the 7 digit serial number 0036849 in ASCII format. 

PM5340 follows the device name for the DHCP server identification instead of MAC ID. 

 

Regards,

Ramasamy N 

See Answer In Context

Attachments
Reply
Reply 1
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2024-03-04 08:45 AM . Last Modified: ‎2024-03-04 08:46 AM

1 Like
0
1137
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-03-04 08:45 AM

Hello @sesa37232_bridg 

The device identifier response from PM5340 for DHCP server 504d353334305f30303336383439 is device name like PM5340_followed by the 7 digit serial number 0036849 in ASCII format. 

PM5340 follows the device name for the DHCP server identification instead of MAC ID. 

 

Regards,

Ramasamy N 

Attachments
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore