Hello,
Client has an application where they supply back to utility network.
I managed to demonstrate that output can be switched when customer is delivering (using Q3 setup with DO1).
Here are things I do not know how to do:
1. is there a logic that can be setup to switch the output at a certain Energy value?
(i.e. at -50kW or at 50kW and not as soon as it switches to Q3)
2. Is there a possibility of adding a software timer in the logic to switch after a preset time?
Thanks,
Yarom
Link copied. Please paste this link to share this article on your social media post.
Thank you Charles.
So you guided me and got a support form L2 who explained how the modules worked.
What worked was to create a setpoint module with the -50kW (Power limits) and use the SUSUNTION for time delay. Then connect that to the Digital output 1 in the module.
Conclusion: Have to get a clearer understanding of ION architecture.
Thanks,
Yarom
Link copied. Please paste this link to share this article on your social media post.
Hello @Yarom ,
1) Have you looked at the different energy values? By default I believe the PM8000 has kW del (power from line to load), kWh rec (power from load to line), kwh del + rec (absolute) and kWh del - rec (net).
2) Have you looked into the Time of Use module (TOU), you can configure up to 4 different rates as different times and days.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Thank you Charles.
So you guided me and got a support form L2 who explained how the modules worked.
What worked was to create a setpoint module with the -50kW (Power limits) and use the SUSUNTION for time delay. Then connect that to the Digital output 1 in the module.
Conclusion: Have to get a clearer understanding of ION architecture.
Thanks,
Yarom