PM8000 display of other voltage when wired single phase

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • PM8000 display of other voltage when wired single phase
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
498
Ramasamy_N
Captain Ramasamy_N Captain
115
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
99
Robert_Lee
Admiral Robert_Lee Admiral
92
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Yarom
Lieutenant JG Yarom Lieutenant JG
Lieutenant JG

Posted: ‎2025-07-23 01:19 AM

0 Likes
6
156
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-23 01:19 AM

PM8000 display of other voltage when wired single phase

Hello,

 

I have a PM8240 in which I wanted to demo for one of our sales guys.  They wanted to see how the measurents can be read.

 

I connected a unit I have with 230VAC control supply. I took V1 and VN from the same supply to show a Voltage reading on the meter's display, Webpage and ION Setup.

 

I set the Volts Mode to Single.

PT Pri = Sec

CT left as is - no current being injected.

 

For some reason, I get a reading on Vb, a little more than half of V1.  See the images.

 

VLL (Vll ab (V)) = 115.10

Vln a (V) = 233.90 [the right reading]

VIn b (V) = 132.47 [Where does this come from?]

V L-N Average = 183.19 [average of a and b]

 

I wanted to see if this is normal so connected PM5350P and PM2200 that I have as well.  Both have Power System option 1PH2W LN, which is the way wired them, identical to PM8240.  Both of the low end PM's showed only the 230V measurement.

 

What am I missing? I am trying to find the details about what SINGLE (Volts Mode) means in the manual. Is there some internal capacitor that is causing the reading? If so, why would the unit not be programmed such that it should disregard that value and display only V1 N?

 

If I may, I have a secondary question - what is the difference between U and V? I am seeing some answers online but none are concrete.

 

Thank you.

 

Yarom

Attachments
Labels
  • Labels:
  • PM5000
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Next Topic

Accepted Solutions
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2025-07-23 07:51 AM . Last Modified: ‎2025-07-23 08:11 AM

0 Likes
2
149
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-23 07:51 AM

Hi @Yarom 

 

There is one phenomenon called Phantom Voltage which is also called as Ghost voltage.

 

Here is an article that clarifies the Phantom Voltage Phenomenon(Voltage readings on unconnected voltage input), which can be observed in meters without ground connections like the PM8000 and PM5000.

 

The Phantom Voltage phenomenon is a normal artifact of the design and is known as Phantom Voltage. This means that in some installations, protective class II PMDs (Power Monitoring Devices) without earth (ground) connections may exhibit 'phantom voltage' readings on unconnected voltage inputs.

Phantom Voltage can be seen on PM8000 and PM5500 series meters that do not have Earth terminal.

 

In the following FAQ, you will find additional detailed information regarding phantom voltages. The FAQ includes the Schneider Electric Technical Reference Phantom Voltage White Paper 7EN52-0331-01, entitled 'Phantom Voltage Readings on Power Monitoring Devices (PMDs).’

https://www.se.com/eg/en/faqs/FAQ000133551/

 

In PM5500, we can minimize the displayed phantom voltage by adding the ground module into the meter. 

Please refer to the Ground Module Installation Guide for more details. The commercial reference for the ground module is "METSEPM55GRMD".

Mehran_Mehrnia_0-1753281051676.jpeg

 

https://www.se.com/ca/en/download/document/NVE30698/

https://www.se.com/ca/en/download/document/METSEPM55GRMD_3D/

 

Regarding the second question, if you check the Display Option Module in ION Reference -> Display Option Module, -> Setup Registers -> Measurement Symbols, you will see the symbol of phase to phase and phase to neutral in IEEE mode are Vll and Vln however in IEC mode are U and V:

 

Mehran_Mehrnia_4-1753282192091.png

 

Mehran_Mehrnia_5-1753282754794.png

 

Best Regards,

-Mehran

L3 Expert Advanced metering

See Answer In Context

Reply
Replies 6
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2025-07-23 07:51 AM . Last Modified: ‎2025-07-23 08:11 AM

0 Likes
2
150
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-23 07:51 AM

Hi @Yarom 

 

There is one phenomenon called Phantom Voltage which is also called as Ghost voltage.

 

Here is an article that clarifies the Phantom Voltage Phenomenon(Voltage readings on unconnected voltage input), which can be observed in meters without ground connections like the PM8000 and PM5000.

 

The Phantom Voltage phenomenon is a normal artifact of the design and is known as Phantom Voltage. This means that in some installations, protective class II PMDs (Power Monitoring Devices) without earth (ground) connections may exhibit 'phantom voltage' readings on unconnected voltage inputs.

Phantom Voltage can be seen on PM8000 and PM5500 series meters that do not have Earth terminal.

 

In the following FAQ, you will find additional detailed information regarding phantom voltages. The FAQ includes the Schneider Electric Technical Reference Phantom Voltage White Paper 7EN52-0331-01, entitled 'Phantom Voltage Readings on Power Monitoring Devices (PMDs).’

https://www.se.com/eg/en/faqs/FAQ000133551/

 

In PM5500, we can minimize the displayed phantom voltage by adding the ground module into the meter. 

Please refer to the Ground Module Installation Guide for more details. The commercial reference for the ground module is "METSEPM55GRMD".

Mehran_Mehrnia_0-1753281051676.jpeg

 

https://www.se.com/ca/en/download/document/NVE30698/

https://www.se.com/ca/en/download/document/METSEPM55GRMD_3D/

 

Regarding the second question, if you check the Display Option Module in ION Reference -> Display Option Module, -> Setup Registers -> Measurement Symbols, you will see the symbol of phase to phase and phase to neutral in IEEE mode are Vll and Vln however in IEC mode are U and V:

 

Mehran_Mehrnia_4-1753282192091.png

 

Mehran_Mehrnia_5-1753282754794.png

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Yarom
Lieutenant JG Yarom Lieutenant JG
Lieutenant JG

Posted: ‎2025-07-23 08:36 AM

0 Likes
1
146
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-23 08:36 AM

Thank you so much for that! That makes perfect sense. We assumed there must be some capacitance and because it is not grounded, there is nowhere for the V to go.

 

The question now becomes, if we know about this and that it is an issue with type 2 power meters, how come can we not have it programmed to recognize the false reading and cancel it out?

Or, for this meter (PM8240), is there somekind of safe and acceptable wiring we can do to avoid the ghost reading?  Otherwise, we have to send a note to each one mentioning this issue and to ignore the reading.

 

(We found the same issue at a VIP - Datacenter that has over a dozen units and some have this type of reading.)

Reply
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2025-07-23 09:15 AM

0 Likes
0
143
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-23 09:15 AM

Hi @Yarom 

 

You're welcome.

 

As verified by the PM8000 offer manager, Phantom voltages may appear unusual, but the meter displays all measured voltages to prioritize safety. Since it can't distinguish between harmless phantom voltages and potentially dangerous ones, suppressing them could pose risks. It's up to safe electrical practices to verify whether a voltage is truly hazardous.

 

You can implement a workaround by activating an alarm when abnormal conditions are detected e.g., voltage present when the breaker is open by using digital inputs to read breaker status signals and correlate them with voltage readings.

 

If eliminating phantom voltage readings is essential, please contact your local Schneider Electric representative for available solutions.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2025-07-23 11:50 AM

0 Likes
2
137
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-23 11:50 AM

Hello @Yarom 
If I am not mistaken, your wiring is V1 only connected to a voltage source correct?
For PM8000 meter, did you connect V2 to V3 to VN?

Charles_Murison_0-1753296491704.png

If V2 and V3 connected to VN, do you still see a voltage on V2?

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Yarom
Lieutenant JG Yarom Lieutenant JG
Lieutenant JG

Posted: ‎2025-07-28 01:51 AM

0 Likes
1
35
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-28 01:51 AM

Hi Charles,

 

I connected V1 to L and VN to N only. I did nothing with V2 and V3.

 

So I have this:

Yarom_0-1753692549488.png

Are you suggesting I should wire like this:

Yarom_1-1753692575251.png

 (Interesting how in the instruction sheet we only see the options:

Yarom_2-1753692610388.png

And not 1PH2W LN.

 

BR

 

Yarom



Reply
Yarom
Lieutenant JG Yarom Lieutenant JG
Lieutenant JG

Posted: ‎2025-07-28 03:15 AM

0 Likes
0
31
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-28 03:15 AM

Hi Charles,

 

I took your suggestion and applied my second drawing where I connect to N and jumper V2 and V3 terminal to N.  That seems to solve the issue:

 

Yarom_0-1753697555855.jpeg

 

Yarom_1-1753697565816.jpeg

Is this what should have been? Is that what I should have understood from the Instruction Sheet that showed 1PH 2W LL?

 

Is this what clears the issue as the "Phantom Voltage White Paper" that Mehran provided?

 

Best regards,

 

Yarom

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of