Hello,
Can you tell me how to configure option module analog ouput of PM8000 using ION Setup?
It is not described well in the user guide, so I was not able to complete.
The customer wants to transfer kW value to 4-20mA analog output, and the maximum value is 150MW.
The problem is that source selection tab is not activated.
Can anyone teach me step by step?
Thank you for your help in advance!
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Please see ION Reference study the Analog Output Module. You need ION Setup or Designer to add this module and link the input into the power meter module to get kW.