ION 7650 Modbus Master Coms Failure

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION 7650 Modbus Master Coms Failure
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
478
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
89
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
sesa56580_bridg
Ensign sesa56580_bridg Ensign
Ensign

Posted: ‎2015-12-17 11:17 AM

1 Like
9
2191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-12-17 11:17 AM

ION 7650 Modbus Master Coms Failure

For the ION 7650 using the Modbus Master feature is there a reconnect timer when the meter loses coms to a downstream device?

Scenario:

A customer is using an ION 7650 to Modbus Master a generator controller.  When they shut the generator down for maintenance, they completely shut it down - including control power.  In doing this, the ION 7650 loses coms to the generator.  When it comes back online - the meter takes 30 minutes to reconnect.

Is there a setting in the meter that controls this?  Retry timer?

Thanks,

Harvey.

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2015-12-18 05:39 PM

1 Like
0
2108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-12-18 05:39 PM

Yes Harvey there is a timeout on Modbus Master communications.  I believe it tries 3 times at 1 min intervals then enters a 30 mins lockout period.  After 30 mins it will try this process again and if functioning will resume normal operation.  If it fails again it will enter a 30 min timer.

I encourage you to contact technical support with your question as I believe they had derived a custom framework that "might" be able to restore communication earlier than the 30 mins ,however I am not aware if it will work in every case.

Brian

See Answer In Context

Reply
Replies 9
Yut
Captain Yut
Captain

Posted: ‎2015-12-17 11:34 PM

0 Likes
1
2108
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-12-17 11:34 PM

Normally the ION7650 as Modbus Master will keep polling the slaves  every 1 second if the Read Now input of the Modbus Device Importer or Modbus Import module  has no connection. It will poll according the source signal that connected to such as Periodic Timer module the polling interval would be the second setting . If the slave device does not present the polling still continue. Please show more detail how the framework for slave polling was design.

Reply
VictorMarincus
Sisko VictorMarincus Sisko
Sisko

Posted: ‎2015-12-18 01:58 AM

0 Likes
0
2111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-12-18 01:58 AM

Hi Harvey,

As Yut mentioned, we need more details about how the framework is programmed in the 7650 / what modules are used and how they are configured.

I would suggest addressing this question to technical support which can perform a deeper analysis of your framework.

Regards,

Victor

Reply
Nabil_Taha
Lieutenant | EcoXpert Master Nabil_Taha Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2015-12-18 06:45 AM

0 Likes
1
2111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-12-18 06:45 AM

I'm assuming they are using Modbus TCP to communicate to the generator. We've run into the same issue had to work around it by making a maintenance mode that disables communication when they are doing maintenance on the generator and then reenable after they are completed with maintenance. I have been told that this should be part of a future firmware upgrade.

Reply
sesa56580_bridg
Ensign sesa56580_bridg Ensign
Ensign

Posted: ‎2015-12-18 10:23 AM

0 Likes
0
2111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-12-18 10:23 AM

Thanks Nabil.  Is the firmware upgrade to fix the reconnection issue?  Do you know who I would contact to get more detail on this?

Thanks,

Harvey.

Reply
Nabil_Taha
Lieutenant | EcoXpert Master Nabil_Taha Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2015-12-18 10:33 AM

0 Likes
1
2111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-12-18 10:33 AM

Try changing the "Modbus TCP idle timeout" under the Ethernet module to something other than zero and testing that. One of my guys says he tested this and it seemed to work better than the work around we were given.

Reply
sesa56580_bridg
Ensign sesa56580_bridg Ensign
Ensign

Posted: ‎2015-12-18 12:04 PM

0 Likes
0
2111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-12-18 12:04 PM

Thanks.  I will forward the suggestion and see if it resolves anything.

Reply
Anonymous user
Not applicable

Posted: ‎2015-12-18 05:39 PM

1 Like
0
2109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-12-18 05:39 PM

Yes Harvey there is a timeout on Modbus Master communications.  I believe it tries 3 times at 1 min intervals then enters a 30 mins lockout period.  After 30 mins it will try this process again and if functioning will resume normal operation.  If it fails again it will enter a 30 min timer.

I encourage you to contact technical support with your question as I believe they had derived a custom framework that "might" be able to restore communication earlier than the 30 mins ,however I am not aware if it will work in every case.

Brian

Reply
sesa57310
sesa57310 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2015-12-21 09:24 AM

1 Like
1
2111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-12-21 09:24 AM

As Brian Bikadi mentioned, there is custom framework available to workaround this unfortunate default functionality in the meter.  Please find all the information that you might need about this in the following KB article:

   WORKAROUND AVAILABLE: Modbus Master module on ION7xxx/8xxx devices disables communications for 30 minute periods in response to communications timeouts ( WORKAROUND AVAILABLE: Modbus Master module on ION7xxx/8xxx devices disables communications for 30 mi... )

Reply
sesa56580_bridg
Ensign sesa56580_bridg Ensign
Ensign

Posted: ‎2015-12-21 09:43 AM

0 Likes
0
2111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2015-12-21 09:43 AM

Thanks Darren!

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of