Le critère à retenir est: Diamètre du tore > 1,4 x Diamètre du faisceau de câbles.
Les préconisations relatives au courant assigné d'emploi maximal, à la section maxi admissible par phase ne s'appliquent pas dans le cas de Vigilohm car nous mesurons des courants différentiels (ces préconisations s'appliquent seulement si le tore est utilisé avec des produits Vigirex).