FAQ_ Tores compatibles avec les Localisateurs Vigilohm
Metering & Power Quality
Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Le critère à retenir est: Diamètre du tore > 1,4 x Diamètre du faisceau de câbles.
Les préconisations relatives au courant assigné d'emploi maximal, à la section maxi admissible par phase ne s'appliquent pas dans le cas de Vigilohm car nous mesurons des courants différentiels (ces préconisations s'appliquent seulement si le tore est utilisé avec des produits Vigirex).