Dears hello,
I would like to communicate with PM5341 according to TCP/IP protocol, but communication setting doesn't cotain. It just contaion BacNet and Enet.
Where can I reach the retaled protocol and how can I connect with the device by this way?
Thannks for your support.
B&R
Ayşegül
Link copied. Please paste this link to share this article on your social media post.
Hello Aysegul,
You can further navigate to Enet menu and configure the TCP/IP communication parameters for in PM5341.
Please follow the below steps specified in the user manual,
Let us know if you need any more support on this topic.
Regards,
Ramasamy N
Link copied. Please paste this link to share this article on your social media post.
Hello Aysegul,
PM5341 supports the Ethernet communication and it must be connected to PC with the CAT 5 and above version of Ethernet cables.
The meter will not communicate if you connect only pin 7 and 8.
Regards,
Ramasamy N
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hello Aysegul,
You can further navigate to Enet menu and configure the TCP/IP communication parameters for in PM5341.
Please follow the below steps specified in the user manual,
Let us know if you need any more support on this topic.
Regards,
Ramasamy N
Link copied. Please paste this link to share this article on your social media post.
Dear Ramasamy,
Thanks for your comment, I have try to connection by IONsetup, but we have 8 pins on Communication port.
Which one of the is + and -? 7. pin or 8. pin?
Could you share the pin's connection schematic please?
Also do I need to use any convertor to connect the device by ION setup?
Thanks for your comment.
B&R
Ayşegül
Link copied. Please paste this link to share this article on your social media post.
Hello Aysegul,
PM5341 supports the Ethernet communication and it must be connected to PC with the CAT 5 and above version of Ethernet cables.
The meter will not communicate if you connect only pin 7 and 8.
Regards,
Ramasamy N