PM5341 TCP/IP COMMUNICATION PORT PROTOCOL

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
AYSEGUL
Ensign Ensign
Ensign
0 Likes
4
1207

PM5341 TCP/IP COMMUNICATION PORT PROTOCOL

Dears hello,

I would like to communicate with PM5341 according to TCP/IP protocol, but communication setting doesn't cotain. It just contaion BacNet and Enet.

Where can I reach the retaled protocol and how can I connect with the device by this way?

 

Thannks for your support.

 

B&R

Ayşegül

 

Attachments
Tags (1)

Accepted Solutions
Ramasamy_N
Commander Commander
Commander

Re: PM5341 TCP/IP COMMUNICATION PORT PROTOCOL

Hello Aysegul, 

 

You can further navigate to Enet menu and configure the TCP/IP communication parameters for in PM5341. 

Please follow the below steps specified in the user manual, 

 

 

Capture.JPG

 

Let us know if you need any more support on this topic.

 

Regards, 

Ramasamy N

See Answer In Context

Tags (1)
Ramasamy_N
Commander Commander
Commander
0
1186

Re: PM5341 TCP/IP COMMUNICATION PORT PROTOCOL

Hello Aysegul, 

 

PM5341 supports the Ethernet communication and it must be connected to PC with the CAT 5 and above version of Ethernet cables.

 

The meter will not communicate if you connect only pin 7 and 8.

 

Regards, 

Ramasamy N

See Answer In Context

Tags (1)
4 Replies 4
Charles_Murison
Picard Picard
Picard
0 Likes
0
1197

Re: PM5341 TCP/IP COMMUNICATION PORT PROTOCOL

@Ramasamy_N  can you help?

 

Thank you,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
Ramasamy_N
Commander Commander
Commander

Re: PM5341 TCP/IP COMMUNICATION PORT PROTOCOL

Hello Aysegul, 

 

You can further navigate to Enet menu and configure the TCP/IP communication parameters for in PM5341. 

Please follow the below steps specified in the user manual, 

 

 

Capture.JPG

 

Let us know if you need any more support on this topic.

 

Regards, 

Ramasamy N

Tags (1)
AYSEGUL
Ensign Ensign
Ensign
0 Likes
1
1189

Re: PM5341 TCP/IP COMMUNICATION PORT PROTOCOL

Dear Ramasamy,

Thanks for your comment, I have try to connection by IONsetup, but we have 8 pins on Communication port.

Which one of the is + and -? 7. pin or 8. pin?

Could you share the pin's connection schematic please?

Also do I need to use any convertor to connect the device by ION setup?

 

Thanks for your comment.

 

B&R

Ayşegül

 

Tags (1)
Ramasamy_N
Commander Commander
Commander
0
1187

Re: PM5341 TCP/IP COMMUNICATION PORT PROTOCOL

Hello Aysegul, 

 

PM5341 supports the Ethernet communication and it must be connected to PC with the CAT 5 and above version of Ethernet cables.

 

The meter will not communicate if you connect only pin 7 and 8.

 

Regards, 

Ramasamy N

Tags (1)