Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84849members
354306posts

PM5341 TCP/IP COMMUNICATION PORT PROTOCOL

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
AYSEGUL
Ensign Ensign
Ensign
0 Likes
4
1218

PM5341 TCP/IP COMMUNICATION PORT PROTOCOL

Dears hello,

I would like to communicate with PM5341 according to TCP/IP protocol, but communication setting doesn't cotain. It just contaion BacNet and Enet.

Where can I reach the retaled protocol and how can I connect with the device by this way?

 

Thannks for your support.

 

B&R

Ayşegül

 

Attachments
Tags (1)

Accepted Solutions
Ramasamy_N
Commander Commander
Commander

Re: PM5341 TCP/IP COMMUNICATION PORT PROTOCOL

Hello Aysegul, 

 

You can further navigate to Enet menu and configure the TCP/IP communication parameters for in PM5341. 

Please follow the below steps specified in the user manual, 

 

 

Capture.JPG

 

Let us know if you need any more support on this topic.

 

Regards, 

Ramasamy N

See Answer In Context

Tags (1)
Ramasamy_N
Commander Commander
Commander
0
1197

Re: PM5341 TCP/IP COMMUNICATION PORT PROTOCOL

Hello Aysegul, 

 

PM5341 supports the Ethernet communication and it must be connected to PC with the CAT 5 and above version of Ethernet cables.

 

The meter will not communicate if you connect only pin 7 and 8.

 

Regards, 

Ramasamy N

See Answer In Context

Tags (1)
4 Replies 4
Charles_Murison
Picard Picard
Picard
0 Likes
0
1208

Re: PM5341 TCP/IP COMMUNICATION PORT PROTOCOL

@Ramasamy_N  can you help?

 

Thank you,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
Ramasamy_N
Commander Commander
Commander

Re: PM5341 TCP/IP COMMUNICATION PORT PROTOCOL

Hello Aysegul, 

 

You can further navigate to Enet menu and configure the TCP/IP communication parameters for in PM5341. 

Please follow the below steps specified in the user manual, 

 

 

Capture.JPG

 

Let us know if you need any more support on this topic.

 

Regards, 

Ramasamy N

Tags (1)
AYSEGUL
Ensign Ensign
Ensign
0 Likes
1
1200

Re: PM5341 TCP/IP COMMUNICATION PORT PROTOCOL

Dear Ramasamy,

Thanks for your comment, I have try to connection by IONsetup, but we have 8 pins on Communication port.

Which one of the is + and -? 7. pin or 8. pin?

Could you share the pin's connection schematic please?

Also do I need to use any convertor to connect the device by ION setup?

 

Thanks for your comment.

 

B&R

Ayşegül

 

Tags (1)
Ramasamy_N
Commander Commander
Commander
0
1198

Re: PM5341 TCP/IP COMMUNICATION PORT PROTOCOL

Hello Aysegul, 

 

PM5341 supports the Ethernet communication and it must be connected to PC with the CAT 5 and above version of Ethernet cables.

 

The meter will not communicate if you connect only pin 7 and 8.

 

Regards, 

Ramasamy N

Tags (1)