Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Need help for ION8600

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Need help for ION8600
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
sesa82148_bridg
sesa82148_bridg Contributor
Contributor

Posted: ‎2019-12-09 05:43 AM . Last Modified: ‎2020-04-22 01:00 AM

1 Like
7
4338
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-12-09 05:43 AM

Need help for ION8600

Dear Group,

 

need help o explain the following.

 

  • The ION meter value today is 8,216,743.93 MWH. See attached photo. The value is for MWH export.
  • in the moddus map, If the KWH is composed of 2 registers, should not be their maximum value is
    2 To the power 32 (4,294,967,296 KWH = 4,294,967 MWH )?
  •  

How this can be configured in the ION? Since 4,294,967 < 8,216,743.93.

 

Attachments
Labels
  • Labels:
  • ION Setup
Tags (1)
  • Tags:
  • ion8600
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sesa82148_bridg
sesa82148_bridg Contributor
Contributor

Posted: ‎2020-01-01 11:55 PM

2 Likes
1
4309
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-01-01 11:55 PM

we got a direction from Anup Surendran Chozhiyattel Thiyyath <anup.surendran@se.com> , to configure the modbus mapping. meaning , to create new 4 registers (4*16 bit = 64 bit).
in this way , the ION will store the values "as is" in these new registers. 

by this way, we can take the full value of the reading, in Watt resolution. 

the max range shall be 2^64 =18446744073709551616 W  = 18,446,744,073,709 MW. that is 2M times grater than the current value. 

 

we shall try this solution and update the case.

See Answer In Context

Reply
Replies 7
Yut
Yut
Leader

Posted: ‎2019-12-12 08:28 PM

0 Likes
1
4330
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-12-12 08:28 PM

You mean this register address 40232 ?

 

Label       Address   Module no.     Module label   No. of registers    Format    Scaling   Scaling Enable

kWh rec   40232            9                     kWh/kVArh              2                      INT32       1/1000         No

 

Use ION Setup connect to meter change to Advance option select Modbus Slave module go to module No. 9 then configure it.

Hope this may help.

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2019-12-20 09:30 AM . Last Modified: ‎2019-12-20 09:31 AM

0 Likes
2
4325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-12-20 09:30 AM

Hello,

 

The scaling of the register also needs to be taken into account, 1/1000 means that the value send via modbus will be 1000 times as large as the value in the register so when the modbus value is divided by 1000, the end result is 3 decimal points. With the default scaling and configuration, the maximum MWH to be sent = ((2^32 )/1000 )/1000) = 4,294.967296. There are a few options. A) link MWH to the modbus slave module, B) Reduce the scaling.

L4 Prime for Advanced metering and Utilities
Reply
sesa82148_bridg
sesa82148_bridg Contributor
Contributor

Posted: ‎2019-12-23 04:42 AM

0 Likes
0
4321
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-12-23 04:42 AM

Dear Yut,

 

thanks for the reply. 

 

  • the meter displays a value of 8x10^6 MWH and still can increase.
  • note : the meter step up file shows the following :
    1. in ION step up software: the scaling found to be "custom"
    2. in ION meter display : the scaling found to be 1000.

 

so, what is the right scaling to choose in ION step up? in order can show bigger values ? (like the 

  • 8x10^6 MWH)

thanks

Reply
sesa82148_bridg
sesa82148_bridg Contributor
Contributor

Posted: ‎2019-12-23 04:59 AM

0 Likes
1
4320
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-12-23 04:59 AM

i agree with you about the maximum value in MWH it can reach with 2 registers.

but the meter now shows this value in its display " 8x10^6 MWH "and still can increase.

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2019-12-30 10:05 AM

0 Likes
0
4313
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-12-30 10:05 AM

Note that inside the meter, the module in question is Float 64 bit number, only the modbus register is 32 bit integer.

L4 Prime for Advanced metering and Utilities
Reply
sesa82148_bridg
sesa82148_bridg Contributor
Contributor

Posted: ‎2020-01-01 11:55 PM

2 Likes
1
4309
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-01-01 11:55 PM

we got a direction from Anup Surendran Chozhiyattel Thiyyath <anup.surendran@se.com> , to configure the modbus mapping. meaning , to create new 4 registers (4*16 bit = 64 bit).
in this way , the ION will store the values "as is" in these new registers. 

by this way, we can take the full value of the reading, in Watt resolution. 

the max range shall be 2^64 =18446744073709551616 W  = 18,446,744,073,709 MW. that is 2M times grater than the current value. 

 

we shall try this solution and update the case.

Reply
Anonymous user
Not applicable

Posted: ‎2020-03-24 03:32 AM

0 Likes
0
4297
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-03-24 03:32 AM

Hi @sesa82148_bridg,

 

Did you find your answer to the replies above?

If yes, please click on "Accept as Solution" at the bottom right corner of the answer which helps you.

You can also thank the members who tried to help you by liking their comments!

 

Have a nice day.

 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore