We are looking for dc voltage measurement of the 35V dc RMS voltage measured with 0.1ms / sample.
Input = 525V, this will be adjust with thyristof bridge for the correct AC voltage 10kHz switching frequency.
We want to measure the dc voltage 0-35v on the place where the red circle is placed below. This we need to read out in pme through modbus. Or with 0-20mA/ 0-10V
Did somebody already measured with this sample time? I don 't find a power meter with this capabilities.
Link copied. Please paste this link to share this article on your social media post.
Hello Jan,
The PM8000 cannot do what you are looking for for a few reasons:
a) Analog input is 30Vpeak
b) Calculations on the analog inputs are done once a second
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello,
Are you looking for DC offset from an AC signal?
Charles
Posted: 2020-03-16 04:19 AM . Last Modified: 2020-03-16 04:20 AM
Link copied. Please paste this link to share this article on your social media post.
It is a dc signal from 35v DC and current 16000A. The current probe is 0-10V = 0-20000A. This we read in the pm8000 analog input.
But we want the 35Vdc measurement connected to the pm8000 so we can calculate the energy.