Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82464members
350023posts

IP address on Ion7550RTU no display

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
brenton_meterlo
Lieutenant | EcoXpert Master Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master
0 Likes
1
192

IP address on Ion7550RTU no display


We have a Ion7550-RTU without a display and we are trying to connect to it to update its firmware. However we believe this ION has had a IP address assigned to it that we do not have access to, since it does not have a display we cannot see or change it from the panel. Is there a way we can find/change back to default settings in ION setup or directly connecting to it so we can update and change the IP address to what we need? All manuals we can find only says the IP address varies on each device. Any help would be appreciated. Thanks


Accepted Solutions
Yu_Diao
Commander Commander
Commander
0 Likes
0
175

Re: IP address on Ion7550RTU no display

U can connect to this RTU through the RS232 port and IONSteup supports to config IP through it.

Sent from my mobile device.

See Answer In Context

1 Reply 1
Yu_Diao
Commander Commander
Commander
0 Likes
0
176

Re: IP address on Ion7550RTU no display

U can connect to this RTU through the RS232 port and IONSteup supports to config IP through it.

Sent from my mobile device.