Hello,
We have a customer who has a current measurement on the high voltage side of his transformer and a voltage measurement on the low voltage site. he wants to combine both measurements on one PM8000 and ask's if it is possible to program a phase shift on the voltage measurements because the transformer cause a phase shift between the primary and secondary. Therefore he gets no correct power and PF...
I don't think this is possible because power is calculated from the core modules in the ION... but just wanned to be shure...
I advised him to make both measurements on the same side of the transformer.
Kind regards
Link copied. Please paste this link to share this article on your social media post.
How about using ITC Module for PT/CT correction ? Please see ION Reference there is an option for phase error compensation it might be useful.