Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION9000 repeats powering up and down

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Re: ION9000 repeats powering up and down
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
571
Mehran_Mehrnia
Mehran_Mehrnia Champion
203
Ramasamy_N
Ramasamy_N Champion
115
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
T.Okada
T.Okada
Contributor

Posted: ‎2024-06-10 11:02 PM

0 Likes
4
1366
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-10 11:02 PM

ION9000 repeats powering up and down

Hi,

 

Our customer asks us to update the firmware because the ION9000 sometimes automatically repeats powering up and down.

(It’s not only one PQM, but some ION9000 units at the customer site are showing this problem.)

*The current firmware version of the ION9000 is 3.0.1 (the firmware is a hotfix from Schneider).

 

Can we resolve this problem by a firmware upgrade?

I found information in the “What’s new” document for versions 3.1.0, 4.0.0, 4.5.0,

but there is no specific information about a bug fix.

 

Do you have any information about this problem?

 

Sincerely @T.Okada 

 

Labels
  • Labels:
  • ION9000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2024-06-12 08:08 AM

0 Likes
1
1311
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-12 08:08 AM

Hello @T.Okada ,

 

Again without knowing the root cause of the power cycle I cannot say if upgrading the firmware will help. You will need to reach out to your local technical support to troubleshoot. Some of the diagnostics needed require help from technical support to collect.

 

The history of bug fixes for the ION9000 is not publicly disclosed. 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 4
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2024-06-11 08:54 AM

0 Likes
0
1342
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-11 08:54 AM

Hello @T.Okada ,

 

"Can we resolve this problem by a firmware upgrade?" It depends on what is causing the meter to power cycle. How long does the mete stay powered on for, seconds, minutes, hours or days?
If you meter power cycles in seconds, you will not be able to upgrade the firmware before meter power cycles. I strongly recommend you contact your local technical support to troubleshoot. If meter needs to be returned you can provide the case number which should make returning meter easier.

 

regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
T.Okada
T.Okada
Contributor

Posted: ‎2024-06-11 05:54 PM

0 Likes
2
1325
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-11 05:54 PM

Hello @Charles_Murison 

 

Thank you for your prompt reply.

Actually, we don't know how long the PQM stays powered on and off,

but the ION9000 does not always repeat powering up and down.

So we have a timing for updating the firmware of ION9000.

In this case, can we resolve this problem by updating firmware?

 

Another question, can we see the information about revision history of bug fix of ION9000 on the web page?

If you have any idea, could you give us the information?

 

Sincerely,

@T.Okada 

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2024-06-12 08:08 AM

0 Likes
1
1312
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-12 08:08 AM

Hello @T.Okada ,

 

Again without knowing the root cause of the power cycle I cannot say if upgrading the firmware will help. You will need to reach out to your local technical support to troubleshoot. Some of the diagnostics needed require help from technical support to collect.

 

The history of bug fixes for the ION9000 is not publicly disclosed. 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
T.Okada
T.Okada
Contributor

Posted: ‎2024-06-23 06:12 PM

0 Likes
0
1253
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-23 06:12 PM

Hello @Charles_Murison

 

Thank you for your kind reply!

I’ll try to updating firmware and if it's not effective, I contact technical support.

 

sincerely,

Okada

 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore