A9MEM3255 energy meters connected in series

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • A9MEM3255 energy meters connected in series
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
477
Ramasamy_N
Captain Ramasamy_N Captain
113
Robert_Lee
Admiral Robert_Lee Admiral
92
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
85
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
Itch
Crewman Itch Crewman
Crewman

Posted: ‎2024-06-11 08:09 PM

0 Likes
3
752
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-11 08:09 PM

A9MEM3255 energy meters connected in series

I have 2 x A9MEM3255 energy meters connected in series with one CT per phase on a switch board. The problem I am experiencing is the current reading on the display of the meters are not the same value. Can someone explain to me why this may be occurring. One party monitors one meter and another party monitors the other on the RS485 ports. They need to record the same value from each meter. The values are way out with each other.

Labels
  • Labels:
  • iEM3000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Itch
Crewman Itch Crewman
Crewman

Posted: ‎2024-06-20 05:02 PM

1 Like
1
681
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-20 05:02 PM

Hi Mehran,

I had the electricians check again and they had wired the meters in parallel with the CT's instead of putting the CT's in series with the 2 meters. They made the changes and now both meters are reading the correct values. 

They also earthed the S2 connection as the wiring diagram of the meters.

Cheers.

Cheers.

See Answer In Context

Reply
Replies 3
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2024-06-19 10:48 AM

0 Likes
2
695
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-19 10:48 AM

Hi @Itch 

 

Please make sure CT ratios, and other config settings as well as wiring and installation are the same on both A9MEM3255 meters.

 

Thank you.

Best Regards,

-Mehran
L3 Expert Tech Support Specialist

Reply
Itch
Crewman Itch Crewman
Crewman

Posted: ‎2024-06-20 05:02 PM

1 Like
1
682
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-20 05:02 PM

Hi Mehran,

I had the electricians check again and they had wired the meters in parallel with the CT's instead of putting the CT's in series with the 2 meters. They made the changes and now both meters are reading the correct values. 

They also earthed the S2 connection as the wiring diagram of the meters.

Cheers.

Cheers.

Reply
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
Captain

Posted: ‎2024-06-21 08:15 AM

0 Likes
0
663
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-21 08:15 AM

Hi @Itch 

Thank you for the update and now it makes sense.
Yes, CT's and PT's secondary grounding ensures safety of personnel and equipment and enhances the reliability of the power system and measuring devices.

Best Regards,

-Mehran

L3 Tech Support Specialist

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of