- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi All,
We were testing ION9000 Transient Module and found that no “Detection Mode” option in the setup register. We have tried v003.001.000 and v004.000.000, but neither of them has. Does anyone know the reason? Thanks
- Labels:
-
ION9000
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi @Stuart_Cheng
‘Detection Mode’ is not present on all meters except ION8650 meters at this time and by default the ‘Waveshape’ method of Detection Mode is used with ION9000/PM8000/ION7400 meters.
Also there is one NOTE statement under each modules in ION Reference indicating:
Best Regards,
-Mehran
L3 Expert Technical Support Specialist
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi @Stuart_Cheng
‘Detection Mode’ is not present on all meters except ION8650 meters at this time and by default the ‘Waveshape’ method of Detection Mode is used with ION9000/PM8000/ION7400 meters.
Also there is one NOTE statement under each modules in ION Reference indicating:
Best Regards,
-Mehran
L3 Expert Technical Support Specialist
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi @Mehran_Mehrnia,
Many thanks for your reply. May I know the reason why the detection mode is only designed for ION8650? Thanks
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
@Stuart_Cheng Will respond in a private message.
Regards,
Charles
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
May I know the same regarding this?
The factory team and I are working on a project with the same device.
Regards,
Yon Khoerul
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello @YonKhoerul ,
Short answer is ION8650 and ION9000 have different code and are not part of the same platform. If you need this feature, contact your sales team to work with them to create a feature request.
Regards,
Charles

