ION8650C current input burden

Metering & Power Quality

Collaborate with multiple experts and discuss various topics about Power Meters and Power Quality. From design & implementation to troubleshooting and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.

Solved
Marcos_Augusto
Ensign Ensign
Ensign
0 Likes
9
1649

ION8650C current input burden

      Does anybody happen to know why has ION8650C Socket burden rocket from 0,05 to 8VA?


Accepted Solutions
AmyRizner
Ensign Ensign
Ensign
0 Likes
1
1592

Re: ION8650C current input burden

Our Marcom team has informed me that this will get fixed in the next revision of the catalog.

As Dan explained, the latest Install Sheets have the correct values.

Hope this helps.

See Answer In Context

9 Replies 9
DanL
Commander Commander
Commander
0 Likes
8
1592

Re: ION8650C current input burden

The CT input burden of the ION8650 Socket meter is 0.05VA at 5A (0.002 Ohm max).

The power supply burden of the ION8650 meter is approximately 8VA (depends on order option and supply characteristics). The ION8650 can be ordered with an auxillary power cord or with an internal 3-phase supply powered from the voltage measurement terminals.

Marcos_Augusto
Ensign Ensign
Ensign
0 Likes
4
1592

Re: ION8650C current input burden

Hi, Dan. Thanks for your reply. I just got this question from a customer, and he sent me the datasheet tables below.

Considering your explanation, the information really looks a bit confused in the table. I totally understand the customer's surprise.

Take a look...

BR

ION_Comp.jpg

DanL
Commander Commander
Commander
0 Likes
3
1592

Re: ION8650C current input burden

Which installation guide is that from?

The latest I can find is here and looks correct.

http://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Id=902333793&p_File_Name=...

Marcos_Augusto
Ensign Ensign
Ensign
0 Likes
2
1592

Re: ION8650C current input burden

Actually it is from a catalogue.

You can check by yourself using the following link:

https://schneider-electric.box.com/s/vbj3b1s64a7nv64yxqmwgroq8s0ujctr

BR

AmyRizner
Ensign Ensign
Ensign
0 Likes
1
1593

Re: ION8650C current input burden

Our Marcom team has informed me that this will get fixed in the next revision of the catalog.

As Dan explained, the latest Install Sheets have the correct values.

Hope this helps.

Marcos_Augusto
Ensign Ensign
Ensign
0 Likes
0
1592

Re: ION8650C current input burden

Ok. I just told that to the customer and sent him the 2015 User Guide.

Thank you, Amy and Dan.

BR

Scott_MCN
Lieutenant
Lieutenant
0 Likes
2
1543

Re: ION8650C current input burden

Hi Dan,

 

What's the burden for the M8650A0C0E6C7C4A? The datasheet gives a typical and maximum value for socket form factor. 

 

 

Regards,

 

– Scott Clysdale

Tags (1)
DanL
Commander Commander
Commander
0 Likes
1
1541

Re: ION8650C current input burden

I've informed @Sanjeet_Sahota about the errors in the technical datasheet: PLSED310027EN_US

The 22/03/2021 version of this document has the "blade power supply" burden spec moved into the current burden section. 

If there are other documents in error, please let him know.

 

The correct specification is:

Socket Current Class 2/10/20
Input-Current burden: 0.05VA per phase at 5A (2 milliOhms max)

 

Switchboard Current Class 2/10/20
Input-Current burden: 0.05VA per phase at 1A (50 milliOhms max)

 

 

Tags (1)
Sanjeet_Sahota
Lieutenant Lieutenant
Lieutenant

Re: ION8650C current input burden

Hi Everyone,


Just to follow up on this topic.  First off, thanks @DanL for providing the correct information.  This information will be corrected in the latest revision of the technical datasheet being released in a few days. 

Best Regards,

Sanjeet