Hello,
The load profile data interval is 5 minuites in the ION8650 meter, is there a way in IONsetup or Vista to view the interval data by 15 minuites without changing the 5 minuites default setting in the meter?
Thanks
Leo
Link copied. Please paste this link to share this article on your social media post.
Hello @Liangchen1982 ,
By default, no, ION Setup does not have aggregate feature. Vista default pages also do not have aggregate feature. However Vista does have the ability to do custom SQL queries. IF you can come up with a SQL query that is able to aggregate the data for you then you could possibly be able to view the aggregated data in Vista.
Sadly I do not know of a specific SQL query to do this aggregation.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Liangchen1982 ,
By default, no, ION Setup does not have aggregate feature. Vista default pages also do not have aggregate feature. However Vista does have the ability to do custom SQL queries. IF you can come up with a SQL query that is able to aggregate the data for you then you could possibly be able to view the aggregated data in Vista.