Hi All,
I am looking for the response time of ION9000 from detecting a specific condition (ex: frequency exceeds a certain threshold) to sending a digital out signal.
I found the following description in the datasheet. May I understand that the response time can be as fast as 1/2 cycle? Thanks
Link copied. Please paste this link to share this article on your social media post.
Hello @Stuart_Cheng ,
You will not find any official, documented response time as a lot will depend on how the meter is configured. High speed (1/2 cycle) conditions require that framework components are High speed modules. This is not to say that High speed modules will allow meter to give X output given Y signal at inputs within 1/2 cycle.
Regards,
Charles
Link copied. Please paste this link to share this article on your social media post.
Hello @Stuart_Cheng ,
You will not find any official, documented response time as a lot will depend on how the meter is configured. High speed (1/2 cycle) conditions require that framework components are High speed modules. This is not to say that High speed modules will allow meter to give X output given Y signal at inputs within 1/2 cycle.