Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

ION7400 historical data management

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • ION7400 historical data management
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
581
Mehran_Mehrnia
Mehran_Mehrnia Champion
216
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
RicardoMiranda
RicardoMiranda
Contributor

Posted: ‎2025-08-13 09:12 AM

0 Likes
3
1401
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-13 09:12 AM

ION7400 historical data management

Hello everyone, nice to meet you.

From Chile, I have the following question regarding the management of the historical data stored by the ION7400 analyzer. Is it possible to manage this historical information and calculate the maximum value of any recorded variable for the month between specific times? This variable must be reset each month.

 

For example, bring the maximum variable (Current) for the month, which occurred between 10:00 and 11:00.

 

I understand that the meter can be programmed with the ION Setup tool, but I don't know if it has these programming capabilities, as it is a very specific task.

 

Thank you very much.

Labels
  • Labels:
  • ION Setup
  • ION7000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
RobGraham
RobGraham Champion
Champion

Posted: ‎2025-08-13 11:47 AM

1 Like
0
1390
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-13 11:47 AM

The ION meter doesn't have any meaningful access to its own logged data.  That said, I can picture an ION framework using a Time of Use Module to enable a Maximum Module to store the maximum value during that period, then reset every month using the Clock module.

 

This is a rather advanced task requiring the use of Advanced ION Setup mode (or, better, PME's Designer application).  I recommend you familiarize yourself with that as well as the modules in the ION Reference before attempting this on a production meter.

See Answer In Context

Reply
Replies 3
RobGraham
RobGraham Champion
Champion

Posted: ‎2025-08-13 11:47 AM

1 Like
0
1390
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-13 11:47 AM

The ION meter doesn't have any meaningful access to its own logged data.  That said, I can picture an ION framework using a Time of Use Module to enable a Maximum Module to store the maximum value during that period, then reset every month using the Clock module.

 

This is a rather advanced task requiring the use of Advanced ION Setup mode (or, better, PME's Designer application).  I recommend you familiarize yourself with that as well as the modules in the ION Reference before attempting this on a production meter.

Reply
Mehran_Mehrnia
Mehran_Mehrnia Champion
Champion

Posted: ‎2025-08-13 12:57 PM

1 Like
0
1389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-13 12:57 PM

Hi @RicardoMiranda 

 

You can also refer to the following existing topic in the Exchange Community on a similar subject, I hope it helps:

how to find the maximum current draw in a month in PM8000

 

As for retrieving the maximum value of a variable (Current) for the month, specifically between 10:00 and 11:00, other modules such as Time Of Use or Arithmetic Modules are needed to configure frameworks that measure for example the demand values for that specific time periods.

 

Best Regards,

-Mehran

L3 Expert Advanced metering

Reply
Yut
Yut
Leader

Posted: ‎2025-08-18 01:55 AM

1 Like
0
1332
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-08-18 01:55 AM

Get into the ION Reference study the Scheduler Module, Maximum module.

You may use ION Setup Advance mode or Designer, for me I prefer Designer.

The TOU can be use but it might interfere the TOU setting. 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore