High Speed ION Module - 1/2 cycle measurements - ION 8650

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • High Speed ION Module - 1/2 cycle measurements - ION 8650
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Picard Charles_Murison Picard
495
Ramasamy_N
Captain Ramasamy_N Captain
115
Mehran_Mehrnia
Captain Mehran_Mehrnia Captain
95
Robert_Lee
Admiral Robert_Lee Admiral
92
View All
Related Products
product field
PowerLogic
PowerLogic ION8650 series

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Solved
rodrigorpgsc
Crewman rodrigorpgsc
Crewman

Posted: ‎2022-01-14 11:13 AM

0 Likes
7
3034
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-01-14 11:13 AM

High Speed ION Module - 1/2 cycle measurements - ION 8650

Hi,

 

We intend to get slow AND also fast measurements at our ION8650. We need request this data at real time and using modbus TCP table.

 

We configure a PLC to act as modbus master and request data each 60ms. So we are able to read VLL avg scaled(address-40184) and kw tot scaled (address-40204), although the meter answer each of our request this values only update at each 1s.

 

This measurement, at 1s rate, is very good for revenenue measurements because don`t show noise. However we would like to know how to read faster measurements too, even with noise.

 

I read the manual a lot and sounds that 8650 allow to measure1/2 cycle (instantaneous measurements). This fast measurement is allow to be request at modbus interface? How to configure 8650 to do that?

  • Thumbnail of PowerLogic ION8650 series
    PowerLogic
    PowerLogic ION8650 series
View products (1)
Labels
  • Labels:
  • ION Setup
  • ION8000
Tags (2)
  • Tags:
  • english
  • Instantaneous measurements
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2022-01-17 09:31 AM . Last Modified: ‎2022-01-17 09:54 AM

0 Likes
6
3013
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-01-17 09:31 AM

Hello @rodrigorpgsc ,

 

You are correct that the ION8650 meter does have some modules that update at a 1/2 cycle rate and other modules that update at 1 second and very few that can be either. The modbus slave modules (used for modbus communications) is a module that only updates once a second regardless of what inputs are connected. There is no way to retrieve data from the meter via modbus any faster than once a second.

 

The protocol DNP can update at the 1/2 cycle rate, but only for a few measurements as configuring the module for 1/2 cycle uses a significate amount of CPU power.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2022-01-19 02:09 PM

0 Likes
1
2972
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-01-19 02:09 PM

Hello Rodrigo,

 

Using ION Setup DNP wizard to setup the DNP could work but may hide some elements from you. I would put meter into advanced mode, add the module, link registers and configure registers manually. This is not a simple task which is why the wizard in ION Setup exists.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 7
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2022-01-17 09:31 AM . Last Modified: ‎2022-01-17 09:54 AM

0 Likes
6
3014
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-01-17 09:31 AM

Hello @rodrigorpgsc ,

 

You are correct that the ION8650 meter does have some modules that update at a 1/2 cycle rate and other modules that update at 1 second and very few that can be either. The modbus slave modules (used for modbus communications) is a module that only updates once a second regardless of what inputs are connected. There is no way to retrieve data from the meter via modbus any faster than once a second.

 

The protocol DNP can update at the 1/2 cycle rate, but only for a few measurements as configuring the module for 1/2 cycle uses a significate amount of CPU power.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
rodrigorpgsc
Crewman rodrigorpgsc
Crewman

Posted: ‎2022-01-17 09:52 AM

0 Likes
0
3008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-01-17 09:52 AM

Charles,

 

Thanks!

 

We`ll try to request using DNP protocol for 1/2 cycle.

Tags (1)
  • Tags:
  • english
Reply
rodrigorpgsc
Crewman rodrigorpgsc
Crewman

Posted: ‎2022-01-17 12:18 PM

0 Likes
4
2999
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-01-17 12:18 PM

5 variable using 1/2 cycle update time and DNP3 sound ok or is too much for CPU ?

Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2022-01-18 10:11 AM

0 Likes
3
2987
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-01-18 10:11 AM

Hello @rodrigorpgsc ,

 

The DNP module itself is not a standalone item. The total CPU usage is also dependent on the rest of the framework on the meter. For example if you do not need EN50160 there is a bit of CPU usage you could save CPU "space" by removing the modules that support EN50160.

 

DNP modules can have up to 4 inputs. If trimming down to 4 measurements is an option that would be easiest. If 5 measurements are a requirement then 2 DNP modules needed. The DNP module at 1/2 cycle update times will use the same CPU usage with 1 measurement linked as 4. Just to keep this in mind when selecting measurements.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
rodrigorpgsc
Crewman rodrigorpgsc
Crewman

Posted: ‎2022-01-18 10:41 AM . Last Modified: ‎2022-01-18 10:51 AM

0 Likes
2
2983
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-01-18 10:41 AM

Hi Charles,

 

Thanks (a lot) for your patience

 

I logging at 8650, using SCH ION setup, and find 34 (`slow`) points at standard DNP map, so the standard map is using 9 dnp modules by standard, don`t?If I don`t erase the default and insert 5 points I`ll use 10 dnp modules, don`t?

 

The rigth place to configure the export of HS is at (I attach a screnshot)

Ion setup->3rd party comm->DNP map setup ->dnp register ->Parameter selection

?

 

I intend to select a HF variable, ex: HS PF lead tot, and put at map to allow my PLC to begin request to request this fast variable

 

 

Attachments
Tags (1)
  • Tags:
  • english
Reply
Charles_Murison
Picard Charles_Murison Picard
Picard

Posted: ‎2022-01-19 02:09 PM

0 Likes
1
2973
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-01-19 02:09 PM

Hello Rodrigo,

 

Using ION Setup DNP wizard to setup the DNP could work but may hide some elements from you. I would put meter into advanced mode, add the module, link registers and configure registers manually. This is not a simple task which is why the wizard in ION Setup exists.

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
rodrigorpgsc
Crewman rodrigorpgsc
Crewman

Posted: ‎2022-01-20 02:31 AM

0 Likes
0
2968
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-01-20 02:31 AM

Thanks Charles!

 

I'll do that.

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of