Hi Evandro,
Connecting a gateway to the Ethernet port doesn't make sense. A gateway converts protocols on the OSI layers e.g. Modbus RTU (RS485 serial) to Modbus TCPIP (Ethernet) - or - BACnet RTU to BACnet IP
I'm not sure whether this will work, it is usually one method or the other, not both. I have not tried it but someone else on the Exchange may have...
Yes, you can have multiple masters on a serial line poll a slave device; however, you may lose packets if both masters try and poll at the same time, limit time between requests from the masters. In your case, the solution may be to connect another gateway to the serial line?