Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Displacement PF and True PF difference at PM5330

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Displacement PF and True PF difference at PM5330
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
Caglar_Abatay
Caglar_Abatay Mentor
Mentor

Posted: ‎2021-02-26 05:55 AM

0 Likes
7
4177
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-02-26 05:55 AM

Displacement PF and True PF difference at PM5330

Hello,

 

We used PM5330 series power meters at our project. There is a wrong values at some points. Displacement PF's are good but  True PF's are low. 

 

What is the difference between Displacement PF and True PF?

How calculate PM5330 Real Power? 

If PM5330 uses the True PF for calculate Real Power, can we change the calculation method of Real Power with Displacement PF?

 

Thanks.

 

 

 

 

 

 

 

Labels
  • Labels:
  • PM5000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2021-03-01 11:16 PM

2 Likes
2
4157
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-01 11:16 PM

Sure @Caglar_Abatay 

 

You can write to the offer marketing manager of this range (Shreesha PANDITH <shreesha.pandith@se.com>) to consider this requirement in future. 

 

Regards, 

Ramasamy N

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 7
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2021-02-26 08:31 AM

0 Likes
1
4174
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-02-26 08:31 AM

Hello @Caglar_Abatay 

 

What is the difference between Displacement PF and True PF?

True power factor includes harmonic content.
Displacement power factor only considers the fundamental frequency.

 

Questions regarding the PM5330 I will need to leave to @Ramasamy_N 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Tags (1)
  • Tags:
  • english
Reply
Caglar_Abatay
Caglar_Abatay Mentor
Mentor

Posted: ‎2021-02-28 10:11 AM

0 Likes
0
4169
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-02-28 10:11 AM

Thank you @Charles_Murison 

 

Hello @Ramasamy_N , Can I change the calculation method of PM5330's Real Power as Displacement Power Factor via ION Setup etc?

 

Best Regards.

Tags (1)
  • Tags:
  • english
Reply
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2021-02-28 09:37 PM

1 Like
4
4165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-02-28 09:37 PM

Hello @Caglar_Abatay 

 

The PM5330 calculates the real power based on True PF value. There is no option to change the power calculation based on Displacement PF. 

 

If the actual waveforms are pure, the True and Displacement PF will be equal. When the load has harmonics, the true PF will be less than the Displacement PF.

 

Regards, 

Ramasamy N 

Tags (1)
  • Tags:
  • english
Reply
Caglar_Abatay
Caglar_Abatay Mentor
Mentor

Posted: ‎2021-03-01 10:04 PM

0 Likes
3
4159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-01 10:04 PM

Hello @Ramasamy_N ,

 

Load has harmonics and  the true PF will be less than the Displacement PF.

It would be great if there was a replacement option of calculation.

 

Best Regards.

 

Tags (1)
  • Tags:
  • english
Reply
Ramasamy_N
Ramasamy_N Champion
Champion

Posted: ‎2021-03-01 11:16 PM

2 Likes
2
4157
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-01 11:16 PM

Sure @Caglar_Abatay 

 

You can write to the offer marketing manager of this range (Shreesha PANDITH <shreesha.pandith@se.com>) to consider this requirement in future. 

 

Regards, 

Ramasamy N

Tags (1)
  • Tags:
  • english
Reply
DanL
DanL Champion
Champion

Posted: ‎2021-03-02 10:01 AM

4 Likes
0
4145
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-02 10:01 AM

It sounds like the feature/quantity you are asking for is called "fundamental active power" and probably also "fundamental active energy".
I believe that gapless measurement (aka. zero blind) of fundamental or any spectral component of a signal is generally thought to be a more advanced feature. All fundamental power quantities (active, reactive, and apparent) are gapless and available by default on the PM8000 series meters.

https://www.se.com/ca/en/product-range-presentation/62252-pm8000-series/

 

Tags (1)
  • Tags:
  • english
Reply
ShreeshaPandit
ShreeshaPandit Explorer
Explorer

Posted: ‎2021-03-04 09:35 AM

1 Like
0
4132
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-03-04 09:35 AM

Thanks @Ramasamy_N 

 

@Caglar_Abatay : We will investigate about the possibility of providing option for calculating power using distortion PF.

 

Regards

 

Shreesha Pandith

 

   

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.