Continue
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • My Subscriptions
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Changing External Numerical Module value by Modbus using Float data type for PM8000

Metering & Power Quality

Schneider Electric support forum about Power Meters (ION, PowerTag, PowerLogic) and Power Quality from design, implementation to troubleshooting and more.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Metering & Power Quality
  • Changing External Numerical Module value by Modbus using Float data type for PM8000
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Charles_Murison
Charles_Murison Champion
582
Mehran_Mehrnia
Mehran_Mehrnia Champion
217
Ramasamy_N
Ramasamy_N Champion
117
View All

Recommended Forums

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Metering & Power Quality
Start a Topic
Solved
TS_Ting
TS_Ting Contributor
Contributor

Posted: ‎2024-06-24 06:24 AM

0 Likes
3
1734
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-24 06:24 AM

Changing External Numerical Module value by Modbus using Float data type for PM8000

How do I set up PM8000 so that I can write a floating point by Modbus to an external numerical module? I want to compare this against a measured value to trigger data recording.

Labels
  • Labels:
  • ION Setup
  • PM8000
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2024-06-24 10:36 AM

2 Likes
0
1705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-24 10:36 AM

Hello @TS_Ting ,

If you look at the modbus map for the PM8000. You can see starting at register 52301, The external numeric registers are only 32bit Integer registers. There is no way to make this a float. However this is ION and often possible to do what you want some other way. You could, for example, have the int32 value link to Arithmetic module that takes the int32 value and divide to get a decimal value. for example, the Arithmetic module takes the input and divides by 1000. To get the 6.123 inside the meter's template you would send the module value 6123.

 

Possible this can get you what you need.

Regards,

Charles

L4 Prime for Advanced metering and Utilities

See Answer In Context

Reply
Replies 3
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2024-06-24 10:36 AM

2 Likes
0
1705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-24 10:36 AM

Hello @TS_Ting ,

If you look at the modbus map for the PM8000. You can see starting at register 52301, The external numeric registers are only 32bit Integer registers. There is no way to make this a float. However this is ION and often possible to do what you want some other way. You could, for example, have the int32 value link to Arithmetic module that takes the int32 value and divide to get a decimal value. for example, the Arithmetic module takes the input and divides by 1000. To get the 6.123 inside the meter's template you would send the module value 6123.

 

Possible this can get you what you need.

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
TS_Ting
TS_Ting Contributor
Contributor

Posted: ‎2024-06-25 06:53 AM

0 Likes
1
1688
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-25 06:53 AM

@Charles_Murison Thanks for your response. I have tested what you have suggested and it works.

 

Just out of curiosity, I understand that the external numerical modules are floating point registers. I have created a custom modbus register to this module and have forced the floating point values using ION Setup and they are coming across properly. Is this custom register read only as I'm unable to write to it?

 

Ext numerical float.png

Reply
Charles_Murison
Charles_Murison Champion
Champion

Posted: ‎2024-06-25 07:50 AM

0 Likes
0
1679
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-25 07:50 AM

Hello @TS_Ting ,

 

When you use a modbus slave module, you are correct that the register is read only. 

 

Regards,

Charles

L4 Prime for Advanced metering and Utilities
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore