Here is a summary of our essential assets on Vigilohm Insulation Monitoring Devices.
If you do not find what you need, you can contact myself or @didiersegura
Posted: 2020-08-24 05:27 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-08-24 05:27 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-08-26 04:53 AM
Link copied. Please paste this link to share this article on your social media post.
Thanks @Madleen_Laclef , @didiersegura!
Really useful links to unlock Vigilohm business!
Link copied. Please paste this link to share this article on your social media post.
Hi Madleen, @didiersegura
I need some support with the IM20-H and its OTD IMDLRDH, so my questions are:
1.- How many IM20-H can you connect to the IMDLRDH´s HMI using modbus RTU??
2.- Can we serve Modbus TCP/IP from the IMDLRDH´s HMI to a system like PME or EBO?
3.- Where can we get the IM20-H firmaware for an upgrade?? (just in case we needed it, since the IMDLRDH installation guide says that its HMI just work with the IM20-H firmware 2.3.0 or later)
4.- How do I do the IM20-H firmware upgrade?
Hope you can guide me,
BR,
HSU
Link copied. Please paste this link to share this article on your social media post.
Hello @Horacio1 ,
Install sheet for IMDLRDH can be found here:
Answers to your questions:
Regards,