Associate AS BACnet Interface IO points with points on the IO bus

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Associate AS BACnet Interface IO points with points on the IO bus
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • Mahmoud_Sayed
    Mahmoud_Sayed
  • GavinHe
    GavinHe
  • DavidFisher
    DavidFisher
  • BillNeville
    BillNeville
  • CraigEl
    CraigEl
  • AbeMeran
    AbeMeran
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
5497 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Associate AS BACnet Interface IO points with points on the IO bus

Picard Product_Support
‎2018-09-11 12:07 PM

Last Updated: Sisko GavinHe Sisko ‎2023-06-20 08:59 AM

Issue

How to associate BACnet IO points created under the BACnet Interface of the Automation Server with IO points on the Automation Server's IO bus.

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Servers 1.4 and above
  • Building Operation Workstation
  • Building Operation Automation Server
  • Building Operation Automation Server Premium
  • Building Operation Automation Server Bundled

Cause

Connect physical IO points to BACnet network controllers.

Resolution

BACnet Association Tool (EBO V3.0 or higher)

BACnet Association Tool will map properties of a central IO point with corresponding properties of a BACnet point. The tool is capable of mapping a single IO point with a single BACnet point, optionally by also creating a BACnet point, and removing the association between IO and BACnet points. To open the BACnet Association Tool, Select the IO Bus or IO Module, BACnet Interface, Application Folder, or the BACnet point, then in the Actions menu, click BACnet Association Tool.

BACnet Association Tool.png
Most useful is the ability to associate multiple IO points with their corresponding BACnet points in one operation. The tool can be run from a variety of different container types in the WorkStation Tree view, including an IO point, BACnet Point, CIO Module, or the entire IO Bus (as shown below). For more information refer to WebHelp articles: Creating and Associating BACnet Points to I/O Points (se.com) and Associating or Updating BACnet Point Associations to I/O Points (se.com)

BACnet Association Tool 1.png

NOTE: Please be aware applying the BACnet Association Tool retrospectively, to an already configured site, can remove bindings to outputs.  For example output bindings in Script or Function Block programs.  As shown below, if the tool is used to create a BACnet Associated point for an output already bound to a program (1) the Requested Value will be replaced by the Associated Value of the BACnet point (2).

BACnet Association 01.png

This is due to how the BACnet Association Tool uses the bindings, where the newly created BACnet point should be used instead of the IO point.  The solution is to update the removed program binding (3) to use the BACnet Associated point value (4).  

BACnet Association 02.png

SBO 1.4 to 2.x

To associate BACnet IO points created under the BACnet Interface of the Automation Server to points in the IO Bus in SBO 1.4 and above...

The association is made via a read reference, so if we think of the two objects as one being the source and the other the destination you configure the association from the destination object so in the case of an output you configure the association from the BACnet object (in this example BO1). In the case of an input, you'd configure the association from the IO Bus input as that would be the destination object, in other words, the recipient of the value.

(NOTE: for versions prior to 1.4 see Bacnet and StruxureWare Building Operation Central IO points)

  1. Create the points. In this example, we are associating an IO output point named 'Digital Output 1' with a BACnet Binary Output named BO1.
  2. From the properties page of the IO Bus point (Digital Output 1 in this example) click on the gear icon to the right of the 'Requested value' field.
  3. In the 'Requested value' editor click the navigation icon (...) to the right of the 'Reference' field and navigate to the 'Associated Value' of the BACnet point.
  4. Save the configuration changes.

Now that the values have been associated setting the BACnet output value (BO1) will drive the IO Bus output (Digital Output 1)

25624i350D7B68724707BF.png

 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (3)
  • Find more articles tagged with:
  • 14934
  • GavinHeward23
  • MahmoudSayed22
Was this article helpful? Yes No
100% helpful (5/5)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore