Bacnet and StruxureWare Building Operation Central IO points
  • Bacnet and StruxureWare Building Operation Central IO points
‎2018-09-11 05:53 AM
Last Updated: Crewman ContentModerator ‎2025-10-10 02:55 AM
Depicting the differences between Bacnet points and Central IO points.
SmartStruxure 1.3 and lower
Explanation of difference in points
Creating Central IO points
  • When you create inputs and outputs in a non-BACnet SmartStruxure system, you simply create the inputs and outputs and then provide programming to control the Requested value. Trends, alarms and graphics would monitor the value property.
  • In a BACnet SmartStruxure system, the inputs and outputs are created under the IO Module in the same way; however an additional point is created in the Application folder under the BACnet Interface Device. On the property page of that point is a field designating the “Associated Value”. You should browse to the appropriate CIO point and select it. At this point all monitoring, display and control of the object should be accomplished with the BACnet point. (It is also possible to make the link between the associated value and the IO value by using the binding tool.)
  • There is no other binding necessary to make the link between the CIO point and the BACnet “proxy” that is created in the application folder.
For SmartStruxure versions prior to 1.4 please see the attached document for some implications and proper method of operation for using the IO associated value property: PSS Building Operation Attachment 14040rev2.pdf
For SmartStruxure 1.4 and above see Associate AS BACnet Interface IO points with points on the IO bus in SmartStruxure 1.4 and above.
  • 14040
50% helpful (1/2)