Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Bacnet and StruxureWare Building Operation Central IO points

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Bacnet and StruxureWare Building Operation Central IO points
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Carl_Slack
    Carl_Slack
  • RobertAndriolo
    RobertAndriolo
  • CraigEl
    CraigEl
  • AbeMeran
    AbeMeran
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2662 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Bacnet and StruxureWare Building Operation Central IO points

Picard Product_Support
‎2018-09-11 05:53 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 10:00 PM

Issue

Depicting the differences between Bacnet points and Central IO points.

Product Line

EcoStruxure Building Operation

Environment

SmartStruxure 1.3 and lower

Cause

Explanation of difference in points

Resolution

Creating Central IO points

  • When you create inputs and outputs in a non-BACnet SmartStruxure system, you simply create the inputs and outputs and then provide programming to control the Requested value. Trends, alarms and graphics would monitor the value property.
  • In a BACnet SmartStruxure system, the inputs and outputs are created under the IO Module in the same way; however an additional point is created in the Application folder under the BACnet Interface Device. On the property page of that point is a field designating the “Associated Value”. You should browse to the appropriate CIO point and select it. At this point all monitoring, display and control of the object should be accomplished with the BACnet point. (It is also possible to make the link between the associated value and the IO value by using the binding tool.)
  • There is no other binding necessary to make the link between the CIO point and the BACnet “proxy” that is created in the application folder.

For SmartStruxure versions prior to 1.4 please see the attached document for some implications and proper method of operation for using the IO associated value property: PSS Building Operation Attachment 14040rev2.pdf

For SmartStruxure 1.4 and above see Associate AS BACnet Interface IO points with points on the IO bus in SmartStruxure 1.4 and above.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Attachments
Tags (1)
  • Find more articles tagged with:
  • 14040
Was this article helpful? Yes No
50% helpful (1/2)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of