Data Center Expert 9.0.0 release notes

Data Center Expert release notes

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • Data Center Expert
  • What's new in Data Center Expert
  • Data Center Expert release notes
  • Data Center Expert 9.0.0 release notes
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
  • What's new in Data Center Expert
  • Data Center Expert 9.0.0 release notes
  • Manage your DCE subscription license in mySchneide...
  • Data Center Expert subscription license FAQ
  • Data Center Expert 9.0.0 Virtual Machine trial sof...
  • Known issues in DCE
  • Data Center Expert 7.9.x and newer - server hardwa...
  • Creating a bootable USB Key (Windows or Linux mach...
  • Data Center Expert release summary
  • Data Center Expert 8.3.0 release notes
  • EcoStruxure IT Data Center Expert 8.2.0 release no...
  • EcoStruxure IT Data Center Expert 8.1.x Release No...
  • EcoStruxure IT Data Center Expert 8.0 release note...
  • Data Center Expert 7.9.3 release notes
  • Data Center Expert 7.9.2 release notes
  • Data Center Expert 7.9.1 release notes
  • Data Center Expert 7.9.0 release notes
  • Data Center Expert 7.8.1 release notes
  • Data Center Expert 7.8.0 release notes
  • Unplugged sensors in DCE 7.4.3
  • What's new in Data Center Expert
  • Data Center Expert 9.0.0 release notes
  • Manage your DCE subscription license in mySchneide...
  • Data Center Expert subscription license FAQ
  • Data Center Expert 9.0.0 Virtual Machine trial sof...
  • Known issues in DCE
  • Data Center Expert 7.9.x and newer - server hardwa...
  • Creating a bootable USB Key (Windows or Linux mach...
  • Data Center Expert release summary
  • Data Center Expert 8.3.0 release notes
  • EcoStruxure IT Data Center Expert 8.2.0 release no...
  • EcoStruxure IT Data Center Expert 8.1.x Release No...
  • EcoStruxure IT Data Center Expert 8.0 release note...
  • Data Center Expert 7.9.3 release notes
  • Data Center Expert 7.9.2 release notes
  • Data Center Expert 7.9.1 release notes
  • Data Center Expert 7.9.0 release notes
  • Data Center Expert 7.8.1 release notes
  • Data Center Expert 7.8.0 release notes
  • Unplugged sensors in DCE 7.4.3

Related Forums

  • EcoStruxure IT Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to Data Center Expert release notes
Start a Topic
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
3949 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Data Center Expert 9.0.0 release notes

Sisko JLehr Sisko
‎2025-09-22 04:04 AM

Part Numbers Affected

  • AP9465
  • AP9470
  • AP9475
  • AP94VMTRL

 

Server hardware requirements have changed in this release.

For the list of the server appliances (AP9465, AP9470, and AP9475) supported by DCE, see

Data Center Expert 7.9.x and newer - server hardware requirements

 

Minimum System Requirements

 

The Data Center Expert desktop client is a stand-alone Java application that runs on systems that meet the following requirements:

 

  • A PC with a 1-GHz or better AMD/Intel processor running a 64-bit operating system: Microsoft® Windows® Server 2019, 2022, and 2025; Windows 10 and 11
  • At least 2 GB of RAM and 20 GB disk space
  • Screen resolution should be set to at least 1024 x 768.
  • Supported browsers: Microsoft Edge; Mozilla® Firefox®; Google Chrome™

Note: See Known Issues in DCE for details about support for Internet Explorer and Edge.

 

New Features

 

Licensing transition

 

As part of Schneider Electric’s initiative to streamline software management across all EcoStruxure IT solutions, your active DCE licenses under support contracts will be upgraded to version 9.0.

 

This upgrade will transition your license management into mySchneider Software Management, which simplifies license handling and provides easier access to the latest software updates.

 

Important: To use this new version, your DCE licenses will be moved to a new licensing model once your current support contract ends. Please note that you will be required to accept new Terms of Use as part of the upgrade process.

 

Contact support to assist you with migrating your licenses. Once you engage with our support team, a Customer Success Manager (CSM) will contact you within 7 days to help align your system and generate updated licenses.

 

After installation and until an updated license is applied, DCE 9.0 will operate in trial mode for 90 days. During that time, some features, such as server upgrades, device firmware updates, and surveillance clip retrieval, will be temporarily restricted. Surveillance clips will continue to be recorded.

 

This release contains improvements including:

 

Increased supported device node count

The maximum supported node count has increased to:

  • AP9465 - DCE Basic server, supports up to 540 nodes (525 nodes + 15 cameras)
  • AP9470 - DCE Standard server, supports up to 2150 nodes (2025 nodes + 125 cameras)
  • AP9475 - DCE Enterprise server, supports up to 4275 nodes (4025 nodes + 250 cameras)

 

Notification on login when attention is required

A notification is shown on login when:

  • An Administrator user does not have an email address associated with their DCE credentials. Administrators can provide an email address in System > Users and Device Group Access.
  • When the DCE server does not have email settings properly configured in System > Server Administration Settings > Email Settings.
  • When the DCE server license is a trial, to notify the user to obtain a license.
  • When the DCE server license has expired, to notify the user to obtain a license.
  • When the password for technical support access is not set.

 

Configurable client inactivity timeout

You can now control how long a user session will remain connected while there is no user-initiated activity in the System > Server Administration Settings > Session Settings option.

This setting applies to both the desktop client and the web client. It is disabled by default. When enabled, the default setting is 5 minutes.

Note: Allowing more than 30 minutes of inactivity is considered a security risk and is not recommended.

 

Improved desktop client startup performance

The desktop client takes less time to load when a large number of devices are monitored.

 

Default file transfer protocol

The default file transfer protocol was changed from FTP only to SCP, Fall back to FTP. You can change the file transfer protocol in Device > SNMP Device Communication Settings > Device File Transfer Settings.

 

Interval offset added in Global Scan Settings

In SNMP and Modbus Device Communication Settings > Global Scan Settings, the next device scan time is now based on the Scan end time plus the Scan interval by default.

Data will be displayed in sensor history at intervals that equal the amount of time the scan takes plus the scan interval. This helps optimize network traffic, particularly when monitoring large numbers of devices.

To display data at the configured interval, select From scan start time.

 

Improved device scan logging

Logging was added for device scan start, scan end, next scheduled scan, and scan paused to diagnose issues more efficiently.

 

Increased default timeout in Device Scan Settings

In SNMP and Modbus Device Communication Settings > Device Scan Settings, the default timeout settings were increased from 2 seconds to 10 seconds to reduce intermittent device communication issues.

 

 

Web client enhancements

  • You can now view historical and active alarm data for all monitored devices on the Devices > Alarm History page. Search by description, device label, device hostname, or status; filter by alarm type, severity and timeframe; and toggle to show or hide resolved and hidden alarms.
  • Logs, desktop client download, status, and help pages were updated to align with the current page design.

 

Description added in Device Group information

There is now a Description field in the Create/Edit Device Group options.

 

Improved capture server logs

Capture server logs now include the routing table.

 

Set backup password

You can now set the password used to encrypt new backup files. Go to System > Server Administration Settings > Server Backup/Restore and click Change Backup Password.

 

File names for failed and successful backups

All backups in progress now have a *.tmp file name until complete. To distinguish failed and successful backup files, failed backups retain the *.tmp file name; successful backups end in *.dce.

 

Added endpoints in the REST API

A minimum value endpoint and a peak value endpoint were added to the REST API to support the Sensor Summary report.

 

Password required for server access by technical support

A password is now required for technical support to access the DCE server to assist with advanced troubleshooting. You must log in to the DCE server console using the apcsetup account to set the support password. You provide that password to the technical support agent if access to the server is required for troubleshooting.

 

Event log enhancements

The event log now includes:

  • Dashboard activity messages when users create, modify, or delete dashboards
  • Authentication server messages when users are added or removed
  • Improved web client access messages when users log in or out

 

Visit the EcoStruxure IT Help Center for more information about Data Center Expert.

 

 

 

Server operating system

 

Server OS: Proprietary Rocky Linux 8.10 (RHEL derivative)

 

Java Version: OpenJDK-headless-17.0.15.0.6-2.el8

 

 

Windows desktop client

 

Java version: Adoptium 8u452-b09

 

 

Software vulnerabilities fixed in DCE 9.0.0

 

The security vulnerabilities addressed in this release include:

 

  • CVE-2025-50125
  • CVE-2025-50124
  • CVE-2025-50123
  • CVE-2025-50122
  • CVE-2025-50121
  • CVE-2025-6438

 

Schneider Electric Security Notification

 

 

The following third-party components were updated to address these specific cybersecurity vulnerabilities:

 

  • CVE-2025-50302 - Linux Kernel
  • CVE-2025-27363 - FreeType
  • CVE-2024-53150, CVE-2024-53197 - USB audio
  • CVE-2024-53104 - UVC Driver
  • CVE-2024-8176 - libexpat

 

This release includes various component updates to improve overall security.

 

See the Data Center Expert Security section in the Help Center for more information.

 

Issues Fixed

 

The following issues were fixed in DCE 9.0.0:

 

  • The capture logs now include all new events as expected.
  • Documentation for System > Server Administration Settings > Storage Settings > Purge Settings was updated to accurately describe the percentage of total capacity that will cause the purge to end. Depending on how data is stored, the actual percentage may be below the configured value.
  • The reset button on the User Preferences page now resets changes to the graph line style as expected.
  • The URL in the Report from line in scheduled email exports is now https://…
  • Test Export in the Reports > Manage Export Scheduling > Export Action Configuration wizard now validates the export settings as expected.
  • DCE requires multiple binds to Active Directory or LDAP systems on login. This can now be reduced for individual users if the AD or LDAP instance utilizes memberOf. If the user is part of a group that is added to DCE, multiple binds are still required.
  • DDF filename formats are now validated during import to prevent server issues caused by unsupported characters.
  • Historical alarms and events are now included in automatic purge.
  • When HTTP is enabled without enabling HSTS on the DCE server, a message advising the user to connect using HTTPS is now displayed.
    Note: If HTTP is not needed, you can modify HTTP and HTTPS settings in the desktop client on the System > Server Administration Settings > Server Access > Web Server tab.
  • In French and Spanish locales, graphs are now displayed correctly in the web client when decimal values use commas.
  • LDAP group members with Administrator privileges can now add or assign dashboards in the web client.
  • The line graph gadget in the web client now handles permission changes correctly.
  • When restoring a DCE configuration backup to a DCE server with a different MAC address, the new MAC address is now updated correctly in the DCE database. Synchronized and Full backups were not affected by this issue.

 

Known Issues

 

  • The Change server and Reboot options do not relaunch the desktop client on Windows 11 and Windows Server 2025.
  • Launch to device from the DCE desktop client may not work as expected. Some modern web UI frameworks are not supported by the internal desktop client browser.
  • Launch to device to NMC3.devices with 3.2.x and 3.3.x firmware does not automatically log in the user.
  • The web client does not show progress as expected when restoring from backup. A message is displayed, Please wait while Data Center Expert initializes. Do not reboot the server while the restore is in progress.
  • If an AD/LDAP user provides a bad password and their system is configured to lock users out after X failed attempts, make sure that X is greater than 3 to account for 3 bind attempts by DCE. This prevents users from being locked out on a single bad attempt.
  • The DCE 9.0 server cannot be updated to the next version while the server is in FIPS mode. Go to System > Server Administration Settings > Server Access > Security Policy and choose a policy other than FIPS before applying the update. Note: The server will reboot after you change the policy.

Complete list of known issues in DCE

 

Release notes for older versions of Data Center Expert

 

 

Upgrade Procedure

 

The following steps are necessary to upgrade Data Center Expert 8.3.0 to Data Center Expert 9.0.0.

 

The Data Center Expert 9.0.0 update performs a data migration that takes under an hour for most systems. The data migration can take up to four hours if the system has thousands of devices and years of history. 

Do not reboot the server during the update.

 

Note 1:  You must have a valid software support contract to receive the Data Center Expert 9.0.0 upgrade.

 

Note 2: Data Center Expert must be at a minimum of version 8.3.0 to upgrade to Data Center Expert 9.0.0.  If you are downloading Data Center Expert 9.0.0, you will need access to the Internet.

 

Note 3: Verify the apcsetup, apcinfo, and apcreset passwords before you begin the upgrade.

 

NOTICE: Before beginning an upgrade, remember to run a full backup on your Data Center Expert. Go to System > Server Administration Settings > Server Backup/Restore, create a backup entry, and then click Start.

 

It is recommended that you perform the server upgrade when you upload the upgrade file to your DCE server. The upgrade will be performed automatically if the server reboots after the upgrade file is uploaded.

 

  1. Download the upgrade.zip file or contact Technical Support for assistance: http://www.apc.com/support/index.cfm.

    Note: The restore.iso file may be needed for later use if a re-installation is required. See Restoring using ISO Format for instructions for restoring your data from a restore.iso file from the ISO format.
  2. Log in to your Data Center Expert 8.3.0 server with full server access. Select Updates > Apply Server Update.
  3. Click Import to import the upgrade.zip file.

Note: Only the zipped upgrade file is accepted.

  1. The Upgrade/New Packages table will update indicating there is an update available for the Data Center Expert server. Check the "Install/Upgrade" option for the package(s) you want to upgrade. Click Install Selected to start the upgrade for the selected package(s). You will be prompted to confirm you want to proceed with the upgrade. Click Install Update to start the upgrade process.

Do not reboot the server during the upgrade process.

  1. When the file transfer completes, Data Center Expert will restart and disconnect the desktop client. You can point a web browser to the Data Center Expert server for status.
  2. When the update is complete, point a web browser to the Data Center Expert server, and select Download Client.

 

 

Restoring using ISO Format (Data Center Expert hardware server only)

 

NOTICE: Only perform the steps in this section if directed to do so by a Technical Support technician.

 

Before You Restore:  A system restore will erase all data and restore the Data Center Expert hardware server to its factory default settings. Please make sure you have a copy of all installed license keys and network settings prior to restore.

  1. Download the restore.iso file to create a bootable USB key or contact Technical Support for assistance: http://www.apc.com/support/index.cfm.

    1. For a USB Key, follow the instructions provided in Creating a bootable USB Key (Windows or Linux machine).
  2. Place the USB key in the USB port of your Data Center Expert server.
  3. Reboot Data Center Expert.
  4. To boot to USB, press F11.

Note: Depending on the model, servers may have a different startup look, with the option to press F11 displayed earlier or later in the boot process. For more information, see the server manufacturer instructions.

  1. Select the boot menu (may be called BIOS Boot Manager, BIOS boot menu, One-time boot menu, One-shot BIOS Boot Menu, One Time UEFI Boot, or similar)
  2. Select your USB Device from the list.

The restore process takes approximately 10 minutes for the 1U Data Center Expert Basic, 15 minutes for 1U Data Center Expert Standard or 25 minutes for 2U Data Center Expert Enterprise. When the restore is complete, you will be prompted to remove the USB key and press Enter to reboot the server.

Once Data Center Expert has restarted, you may configure the Data Center Expert network settings per instructions in the Data Center Expert Installation Guide.

 

Migrating a Data Center Expert hardware server to a virtual appliance

 

To migrate a hardware server to a 9.0.0 virtual appliance, you must work with our Customer Success Management team. You will be connected through Schneider Electric’s Customer Care Center.

 

  1. Perform a backup of the Data Center Expert hardware server, using the Server Backup/Restore option, accessed from the Server Administration Settings option in the System menu.
  2. Deploy the trial version and configure it using the hardware equivalents for the Data Center Expert Basic, Standard, or Enterprise server from which you are migrating. The available disk space for the virtual appliance must be greater than the disk space used by the hardware server. You cannot restore to a virtual appliance with fewer CPU, fewer network adapters, less RAM, or less available disk space than the hardware server. See help for Deploying and configuring a Data Center Expert virtual appliance, and Data Center Expert virtual appliance equivalent configurations.
  3. Perform a restore on the virtual appliance, using the Server Backup/Restore option, accessed from the Server Administration Settings option in the System menu. You cannot restore to a virtual machine other than the Data Center Expert virtual appliance.
  4. Log in to the Data Center Expert client. In the License display, accessed from the Server Administration Settings option in the System menu, click Update license you received.

 

Creating a bootable USB Key (Windows or Linux machine)

 

Instructions for a Windows machine:

  1. Insert a 4GB (or larger) USB key into your system.
  2. Extract the following file to a temporary directory:
    DCExpertUsbFlashRestore_Win_9.0.0.zip
  3. Open a command prompt to the temporary directory using the cd command. The command prompt working directory must be the same location as the extracted files.
  4. Run mkDCExpertRestoreUsbKey.bat <iso image filename>.
    Example: mkDCExpertRestoreUsbKey.bat c:\tmp\restore.iso
  5. Answer the prompts as appropriate.

 

Instructions for a Linux machine:

  1. Insert a 4GB (or larger) USB key into your system.
  2. Extract the following file to a temporary directory:
    DCExpertUsbFlashRestore_Linux_9.0.0.tar.gz
  3. Open a command prompt to the temporary directory using the cd command. The command prompt working directory must be the same location as the extracted files.
  4. Run mkDCExpertRestoreUsbKey.sh <iso image filename>.
    Example: mkDCExpertRestoreUsbKey.sh /tmp/restore.iso
  5. Answer the prompts as appropriate.

 

Third-party USB key scripts:

The USB key scripts used to create USB keys utilize the following software:

 

Software

URL

Windows

Linux

Syslinux

http://syslinux.zytor.com/

X

X

7-zip

http://www.7-zip.org

X

 

GNU sed

http://unxutils.sourceforge.net

X

 

 

 

Was this article helpful? Yes No
50% helpful (1/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore