You can download the latest DCE device firmware update catalog that includes the IEC-certified NMC3 firmware 3.x from theEcoStruxure IT Entitlements portal.
An active support contract for all monitored nodes is required.
If you do not monitor NMC3 devices, you can download the DCE device firmware update catalog (SFSWCDFCF) that does not include IEC-certified NMC 3.x firmware here.
In this release
ats 5G 3.2.0.1
Screens added for frequency/voltage configuration and event counts
Communication over Modbus TCP protocol enabled
nb250 3.2.0.1
Firmware update of the wireless coordinator, routers, and sensors is now supported.
The Read-Only user can no longer access actions on the Device > Wireless sensor network page.
px 3.2.0.1
The Network-Only user permitted actions corrected in Web UI
Incoming BACnet packet sizes validated
Cooling fan outage alarm appears over SNMP
apc hw05 nb250 718
Character limit for the NetBotz Module Name increased
User can be modified via config file
Resolved SNMPv3 issue with monitoring
Go to apc.com for additional release note information.
Data Center Expert 8.3.0 released
January 2025
IMPORTANT: The update from 8.2.0 to 8.3.0 requires that you install a new certificate before you install the software update. See the instructions in the release notes.
You can download the latest DCE device firmware update catalog that includes the IEC-certified NMC3 firmware 3.x from theEcoStruxure IT Entitlements portal.
An active support contract for all monitored nodes is required.
If you do not monitor NMC3 devices, you can download the DCE device firmware update catalog (SFSWCDFCF) that does not include IEC-certified NMC 3.x firmware here.
In this release
su hw21 3.2.0.8
NMC3 platform & Smart-UPS are IEC 62443-4-2 certified.
Added config file integrity checking
SSH and Telnet terminate as expected
sucan hw21 3.2.0.5
NMC3 platform & Smart-UPS Ultra are IEC 62443-4-2 certified.
Support added for Modbus TCP/RTU
Added config file integrity checking
su hw21 2.5.3.3
Japanese Event Log web download fixed
Multiple security enhancements
sucan hw21 2.5.3.2
Japanese Event Log web download fixed
Japanese On Battery web status message fixed
Multiple security enhancements
sumx hw05 718
User can be modified via config file
UPS SKU added to PCNS communication
Resolved SNMPv3 issue with monitoring
sy hw05 718
User can be modified via config file
Resolved SNMPv3 issue with monitoring
Modbus -rDefand userdflt-d CLI commands work as expected
sy hw21 2.5.3.2
Japanese Event Log web download fixed
Multiple security enhancements
sy hw21 3.2.0.7
Support added for optional Spot Fluid Sensor
Universal I/O sensor config through CLI
Audit logging entries added to event log
SSH and Telnet terminate as expected
Go to apc.com for additional release note information.