Xenta 527 considerations when used with TAC Vista and I/NET

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Xenta 527 considerations when used with TAC Vista and I/NET
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • CraigEl
    CraigEl
  • RobertAndriolo
    RobertAndriolo
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2337 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Xenta 527 considerations when used with TAC Vista and I/NET

Picard Product_Support
‎2018-09-10 01:28 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 05:21 AM

Issue

What are the limitations of the Xenta 527 when used with TAC Vista and I/NET.

What do I need to consider when integrating I/NET with TAC Vista.

Product Line

TAC INET, TAC Vista

Environment

  • TAC I/NET
  • TAC Vista 5.1.6 and above
  • TAC XBuilder
  • TAC Xenta Server 527 5.1.6 and above
  • I2V

Cause

Integrating I/NET into Vista.

Resolution

Below are a few considerations associated with the Xenta 527 Server that may assist when integrating existing I/NET systems with TAC Vista:

  • As in all case the latest versions of both hardware and software should be used on any integration project.
  • The attached datasheet indicates that the TAC Xenta 527 Web Server has been tested with up to 1000 I/NET points, if you require to integrate more points than this it is then recommended to add additional Xenta Servers to cater for this.  You may also consider segregating your I/NET System to improve performance.
  • Currently it is not possible to pick and choose which points are imported into the XBuilder project, it can only be limited to which SAV file (or controller) is imported .
    Note: Each I/NET point type, as shown below, creates the following number of TAC Vista objects - these include; Alarm, State, Value, Control, Test, Manual, Alarm_ack etc, and vary according to the point type used.
I/NET Point Type Number of TAC Vista
Objects created
DO 14
AO 11
AI 10
PI 10
DI 11
DA 11
   

The impact to consider here is the time it takes when adding or modifying your Xbuilder Project. This usually means that importing a large number of SAV files will cause the Vista server to get extremely busy creating / importing all of these objects.  It is best to let the process complete before selecting any other window.  Note that the total number of objects created during the import of the I/NET points is not counted as part of the 'tested' 1000 point limit stated in the above datasheet. This is a separate consideration.

  • Network performance can be affected when a large number of connection objects are in use (so direct transfers between I/NET and Vista). There is no documented limitation, but the recommendation is not to exceed 300 connection objects per Xenta 527 Server.  For information on what the effects a connection object on the I/NET controller LAN has and how to calculate this, refer to Connection Objects in Xenta Server effect on I/NET system.
  • Engineering of any I/NET feature apart from Point Control, Trends, Time Schedule and Alarm Configuration can only be done using the I/NET Host Tool or via an I/NET workstation.  Access to these features are via the Xenta 527 web server feature, so pages appear as HTML pages within TAC Vista, this will have a different look and feel to both Vista and I/NET users.  

Other Knowledge Base Articles as listed below are also available to assist on integrating I/NET and Vista:

  • Unit conversions when integrating LON to I/NET
  • Vista to I/NET Integration Tips   
  • Decoding the I/NET signal "flags" attribute
  • Viewing I/NET Point Names in Vista Workstation instead of Addresses
  • User Defined Units on I2V integration were accidentally set incorrectly
  • SQL Host not passing data to Xenta 527 Web Server
Labels (2)
Labels:
  • TAC INET
  • TAC Vista
Attachments
Tags (4)
  • Find more articles tagged with:
  • 6015
  • inet
  • Limitations of the Xenta 527
  • vista
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of