Vista to I/NET Integration Tips
  • Vista to I/NET Integration Tips
  • Cody_Failinger
    Cody_Failinger
‎2018-09-06 02:31 PM
TAC INET, TAC Vista
  • I2V Integration
  • I/NET
  • XBuilder
  • Xenta 913
  • Xenta 527
An input in I/NET can only be controlled from an outside source if it is in "Test" or "Manual," so outputs must be used.
When integrating with an I/NET system using a Xenta 5/7/9xx, all I/NET points must be defined as either AO or DO, regardless of the direction of information flow.
To get data from an I/NET system (into Lon, BACnet, or Modbus) use the AO attribute "value" or DO attribute "value."
To get data into an I/NET system (from Lon, BACnet or Modbus) use the AO attribute "value" or DO attribute "control."
Labels (2)
  • TAC INET
Tags (3)
  • 3742
  • inet
  • pass
100% helpful (1/1)