Issue
Vista to I/NET Integration Tips
Product Line
TAC INET, TAC Vista
Environment
- I2V Integration
- I/NET
- XBuilder
- Xenta 913
- Xenta 527
Cause
An input in I/NET can only be controlled from an outside source if it is in "Test" or "Manual," so outputs must be used.
Resolution
When integrating with an I/NET system using a Xenta 5/7/9xx, all I/NET points must be defined as either AO or DO, regardless of the direction of information flow.
To get data from an I/NET system (into Lon, BACnet, or Modbus) use the AO attribute "value" or DO attribute "value."
To get data into an I/NET system (from Lon, BACnet or Modbus) use the AO attribute "value" or DO attribute "control."