Unable to login to Security Expert using Windows Authentication

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Unable to login to Security Expert using Windows Authentication
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • GavinHe
    GavinHe
  • Mahmoud_Sayed
    Mahmoud_Sayed
  • Product_Support
    Product_Support
  • AdamSteele
    AdamSteele
  • RobertAndriolo
    RobertAndriolo

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
3084 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Unable to login to Security Expert using Windows Authentication

Picard Product_Support
‎2018-09-10 10:19 AM

Last Updated: Administrator CraigEl Administrator ‎2023-04-03 06:03 PM

Issue

Windows authentication is not working with Security Expert once configured.

Product Line

EcoStruxure Security Expert

Environment

  • Security Expert Server
  • Windows Authentication

Cause

Windows authentication was not installed or configured properly during initial install/setup of Security Expert.

Resolution

  1. Install the Security Expert Server, and any Security Expert Clients, with the "Enable Windows Authentication" option enabled during the installation process. If this was not initially done at install then it will be required to backup the SecurityExpert and SecurityExpertEvents databases, uninstall Security Expert (installing overtop or repairing install may not work) and then re-install Security Expert with the "Enable Windows Authentication" option enabled.  Refer to Determining Security Expert authentication settings after installation to determine the authentication used.

    01 - Select Windows Authentication.png

  2. When Windows Authentication is enabled in the client go to Global (1) and select Operators (2). 

    02 Global Operator.png

  3. Create a new operator as below:

    1. Select to add a new operator (1). 

    2. Enter a Name (2).  The name does not need to be the same as the operator's username.

    3. Enter a UserName (3).  The username must match the domain name and domain username required to have access to Security Expert.  This is in the form of "DomainName\UserName" as shown in the example image.

    4. Set a Role for this operator (4).

    5. Enable the "Use Windows Authentication" checkbox (5) and save the changes.

      03 Create Operator.png

  4. Go to Global (1) and select Home (2) and logout of Security Expert.

    04 Global Home.png

  5. On the login page select the "Use Windows Authentication" checkbox (1), set the Server to the Security Expert Server machine name (2).  Leave this blank if it is the local machine) and press Log in (3).

    05 Login Windows Authentication.png

  6. The system should now be logged into Security Expert with the Windows username being used.

 

If an "Access Denied" is received or another error then confirm the following before contacting Product Support for further help.

  1. Ensure Security Expert Client and Server were installed with the "Enable Windows Authentication" option enabled.  Refer to Determining Security Expert authentication settings after installation to determine the authentication used.
  2. There is an operator object created in Security Expert with the same domain and user name as the domain user required for login.
  3. The "Use Windows Authentication" option is enabled on this operator object.
  4. At the login screen "Use Windows Authentication" is enabled and the Server is set correctly.
Labels (1)
Labels:
  • EcoStruxure Security Expert
Tags (5)
  • Find more articles tagged with:
  • 19468
  • AdamSteele24
  • ChrisAsbury22
  • GavinHeward23
  • MahmoudSayed22
Was this article helpful? Yes No
100% helpful (5/5)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore