LonMaker menu not shown in Visio when you open LonMaker 3.13 or 3.2

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • LonMaker menu not shown in Visio when you open LonMaker 3.13 or 3.2
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • RandyDavis
    RandyDavis
  • Trey_Boothe
    Trey_Boothe
  • CraigEl
    CraigEl
  • PeterLarsen
    PeterLarsen
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1958 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

LonMaker menu not shown in Visio when you open LonMaker 3.13 or 3.2

Picard Product_Support
‎2018-09-10 10:15 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 01:14 AM

Issue

When opening LonMaker the LonMaker Menu list is not shown in Visio.

Product Line

TAC Vista

Environment

  • Echelon LonMaker 3.xx
  • Microsoft Visio 2002, 2003, 2007, 2010
  • Microsoft Windows XP SP3

Cause

Echelon LonMaker was not installed with Administrator rights or some of the default security settings have been changed.

Resolution

Older versions of Visio - Check the File Paths and Security Settings

  1. Open up Microsoft Visio on its own. Go to Start > Programs > Microsoft Office > Microsoft Visio. (Do not open up Visio by opening up the LonMaker project)
  2. Go to the Tools menu > Options and then select the Advanced tab.
  3. Click the File Paths button. (For LonMaker 3.1, go to Tools > Options > File Paths)
  4. In the Add-ons field make sure that the file path starts with DRIVE:\LONWORKS_PATH\LonMaker. The default path is C:\LonWorks\LonMaker. The path in the Templates and Stencils fields should DRIVE:\LONWORKS_PATH\LonMaker\Visio. The default is C:\LonWorks\LonMaker\Visio.
  5. The next setting to check is the Macro Security. Go to the Tools menu > Options > and then select the Security tab. Make sure that all of the below options are selected.
    • Enable Microsoft Visual Basic for Applications
    • Enable Microsoft Visual Basic for Applications project creation
    • Load Microsoft Visual Basic for Applications projects from text
    • Enable COM add-ins
    • Enable Automation events

 

Newer versions of Visio - Check the File Paths and Security Settings

  1. Open up Microsoft Visio on its own. Go to Start > All Programs > Microsoft Office > Microsoft Visio. (Do not open up Visio by opening up the LonMaker project)
  2. Select "Options" on the left hand side of the window.
  3. Click on the "Advanced" section and scroll down to the bottom. Verify that the "Enable Automation events" box is checked. Click on "File Locations..."
  4. In the Add-ons field make sure that the file path starts with DRIVE:\LONWORKS_PATH\LonMaker. The default path is C:\LonWorks\LonMaker. The path in the Templates and Stencils fields should be DRIVE:\LONWORKS_PATH\LonMaker\Visio. The default is C:\LonWorks\LonMaker\Visio.

Uninstall LonMaker and reinstall with the administrator account used to log into Windows.

The following articles have information about another problem that can cause the same issue:

  • Visio menu not displaying properly after installing Lonmaker 3.1 with Visio 2002 
  • Visio will open but LonMaker menu is missing from the toolbar, the features are unavailable, or Erro... 

There are two other things you may try before uninstalling, that have solved the issue in some cases:

  1. Right-click any toolbar, Choose Customize > Toolbars tab, Choose the Menu Bar, Choose Reset
  2. Remove all registrations in the Tools menu, click Options, and then on the Advanced tab, click File Paths.
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 8280
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore