IT Expert alarm notification policies
Alarms
How to configure alarm thresholds and alarm notification policies, mute and acknowledge alarms, and test email notifications sent from EcoStruxure IT Expert
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
IT Expert Administrator users can configure alarm notification policies to inform specific users in their organization about alarms that occur on monitored devices.
Alarm Notifications
A Default notification policy is pre-configured that includes all groups, locations, categories, and device types, and alarms with critical severity.
You can modify the default notification policy or delete it if you do not want to receive notifications.
Go to Alarms > Alarm notifications.
Click New policy.
Provide a name for your notification policy, and click Create policy.
Select at least one recipient group or email address, at least one location, and the alarm severities, categories, and device types to include in the notification policy.
Click Save.
Individual recipients will receive email notifications once their email address is verified.
Check the box to also notify users for clearing alarms.
Group recipients for notifications are based on group permissions already created in IT Expert.
ITE users specify whether to notify on clearing alarms in their profile > Notifications.
Resolve conflicts during configuration
Conflicting selections are highlighted to make it easier to decide whether to edit permissions or create an additional policy to achieve the desired result.
For example, a group might not have permissions for the locations you selected. See IT Expert permissions
Recipients
Click Select recipients to choose the group(s) or individual email recipients to include in the notification policy.
Groups
Group recipients for notifications are based on group permissions already created in IT Expert.
Selections in the Groups section take precedence over selections in all other sections in the policy.
You can click Add emails to add recipients who are not members of a group in IT Expert.
No group permissions can be assigned to these recipients.
An verification email is sent to each address to confirm it is valid.
No alarm emails are sent to these recipients until their email address is confirmed.
You can resend the verification email if needed.
Location
Click Select locations to choose the location(s) to include in the notification policy.
Users in some groups may not have permissions for all the locations you select. Check user group permissions on the Administration > Groups tab to adjust. You might need to create an additional policy to achieve the desired result. See IT Expert permissions
There is information displayed on the page when any selections in the policy are invalid.
Severity
Select the alarm severities to include in the notification policy: Critical, Warning, or both.
Category
Select the alarm categories you to include in the notification policy: Power, Environment, Infrastructure, Security, and Uncategorized. See IT Expert alarm categories
Device type
Click Select devices to choose the device types to include in the notification policy.
Correct missing information in an existing policy
A warning is displayed in the policy when any option is invalid, for example, if a group or location selected in a policy was deleted from the system.
Click the policy to make the necessary changes.
Alarm notifications details
7969757470237_6801824457629.png
The My profile > Notifications tab allows you to choose whether you want to receive email notifications, push notifications in the EcoStruxure IT mobile app, and cleared alarms.