We have hundreds of MTN6215-5910 modules in our building, and some of them are losing their configuration after being turned off and restarted. Do you know if there's any fix that can be applied to correct this issue?
- Labels:
-
SpaceLYnk
-
Wiser for KNX
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello
There is new firmware available. See https://www.se.com/uk/en/download/document/MTN6215_MTN6216-xxxx_firmware/.
Please check the instruction file whether this might help you.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello Matheuspinheiro,
can you please provide more information about the devices please?!
Which ETS-Application you are using?
Which HW-Version you have installed?
Please make a startup picture of the screen when disconnect a Multitouch and reconnect after some seconds.
Attention: You need to be quick with the foto as the information screen will last only some seconds!
Thomas
Application Design Engineer
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello
There is new firmware available. See https://www.se.com/uk/en/download/document/MTN6215_MTN6216-xxxx_firmware/.
Please check the instruction file whether this might help you.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello Thomas,
We are using a ETS 5.7.7, ETS Version 14, FW version = 26.1 and FS version = 2.10.
Thanks for helping
Kind regards
Matheus
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello Heribert,
Thanks for helping.
I didn't understand the procedures for upgrading. Do I need to use MultitouchUpdater software to update the firmware?
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello Matheuspinheiro
Yes correct. FW update can only be done with Multitouch Pro updater tool.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hello Matheuspinheiro,
in the manual (you can find with the link below), starting on page 143, is the process better described I think.
Please let us know when you still have problems.
Thomas
Application Design Engineer